I am going to wire a 220 v compressor in my detatched garage 60`from the service panel. I tried to test it from an 8000/10000 watt Dewalt generator w/ 30 amp outlet. The compressor has a start and run capacitor w / on / off switch. The compressor will start to run (about 1 sec and trip the 30amp breaker on the Generator. Motor is rated @ 5 hp 18 amp. With the belt off the comp the motor starts and runs immediately. Do I need to use 40 amp breaker for this it seems big for this 60 gal compressor, or is the Generator just not able to run the compressor?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Generator can't handle the startup load. If motor data label shows 5hp the compressor needs to be hardwired using #10 thhn in conduit or #8 nm. 5hp per the NEC needs 35A rated supply conductors, so use minimum of 40A breaker. You can upsize the breaker to handle startup load provided the motor has its own overload protection.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,977
Location
Fargo, ND
I question the 5 HP claim. At 18 amps @ 240 volts I would give it 3-1/2 or 4 HP.

There are a lot of 3.7 HP motors out there on compressors that amp out around that 18 amp number.

To the OP the compressor might run the compressor but it is not wired to run that large of load. You can not simply replace the breaker. You need a larger generator and smaller compressor.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
I am going to wire a 220 v compressor in my detatched garage 60`from the service panel. I tried to test it from an 8000/10000 watt Dewalt generator w/ 30 amp outlet. The compressor has a start and run capacitor w / on / off switch. The compressor will start to run (about 1 sec and trip the 30amp breaker on the Generator. Motor is rated @ 5 hp 18 amp. With the belt off the comp the motor starts and runs immediately. Do I need to use 40 amp breaker for this it seems big for this 60 gal compressor, or is the Generator just not able to run the compressor?
18a is smaller than 5hp... gonna be closer to 3.5-4hp

Having said that, the in-rush current of a motor can be anywhere from 4-8x the FLA. so your genny doesnt have enough surge power to start it...
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,977
Location
Fargo, ND
Having said that, the in-rush current of a motor can be anywhere from 4-8x the FLA. so your genny doesnt have enough surge power to start it...
I sold gerarators for some time. the manufacturers we sold recommended 2-1/2 to 3 times rated amps for motor starting. A 10K generator should start it, 12K would be better, but it isn't his wired for that large of a load.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
I sold gerarators for some time. the manufacturers we sold recommended 2-1/2 to 3 times rated amps for motor starting. A 10K generator should start it, 12K would be better, but it isn't his wired for that large of a load.
umm

18a * 2.5 = 45a
10Kw / 240v = 41.7a

The in-rush current is likely higher than 2.5x FLA so...
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,977
Location
Fargo, ND
umm

18a * 2.5 = 45a
10Kw / 240v = 41.7a

The in-rush current is likely higher than 2.5x FLA so...
He is 800 watts short. It isn't a hard and fast rule, but with an air compressor that pretty much starts under load it might be a bit much. Either way the generator breaker will not handle the load so it doesn't make a difference. A 4 HP motor running a fan I would bet the generator would run it.
 
OP
J

J Tranc

New member
Joined
Jan 16, 2023
Messages
2
Thanks every one for your replies. I`ll run a dedicated line to the garage
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That will be another can of worms! You will need to over size the wiring for the compressor. Does the motor nameplate show a HP?
Why do you say he needs to oversize the wire? It needs to be the correct size based on HP if the motor data shows the actual HP.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,977
Location
Fargo, ND
Why do you say he needs to oversize the wire? It needs to be the correct size based on HP if the motor data shows the actual HP.
You don't size the wire by the amp draw, You size it by motor HP. Most guys will go by the amp draw.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You don't size the wire by the amp draw, You size it by motor HP. Most guys will go by the amp draw.
If you'd said that in the first place I wouldn't have questioned what you were saying. Simply saying that the conductors needed to be oversize wasn't saying why.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,306
Location
Coronado, CA
Generator and small engine power ratings are about as reliable as the “Detroit Horsepower” ratings. IMHO, They should be taken with plenty of Salt.

My little generator was built from an engine rated at 13 horse power and it spins an alternator rated at 10 KW Peak.

I am guessing that the combination is probably good for an honest 6 KW.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,977
Location
Fargo, ND
If you'd said that in the first place I wouldn't have questioned what you were saying. Simply saying that the conductors needed to be oversize wasn't saying why.
I wasn't going into specifics because I don't know the specifics, just tossing out a warning.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,370
Location
Coastal NJ
Generator and small engine power ratings are about as reliable as the “Detroit Horsepower” ratings. IMHO, They should be taken with plenty of Salt.

My little generator was built from an engine rated at 13 horse power and it spins an alternator rated at 10 KW Peak.

I am guessing that the combination is probably good for an honest 6 KW.
Probably about right. Generally takes about 2HP of engine per kW of generator power.
 

no704

Well-known member
Joined
Apr 27, 2016
Messages
5,275
He said he tested it with the generator.

Run an oversized line out and install a sub panel! This is GJ!
 