Wire Ampacity , Temperature Ratings.

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
I will be installing a 8500W heater on a 40A CB. According to this it looks like I can use #10 THHN or THWN-2. But according to Wire & Cable Your Way its only good for 30 A. So which is it?

1760276293797.png

1760276748544.png
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,010
Location
NJ
You actually need a wire good for 44A. (125% of full load)
You use the 60c or 75 c column for ampacity almost exclusively. Since you are showing thhn, use the 75C column.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,218
Location
SE MI
First time I have seen a table that allows 25A on a 14AWG wire ! (yes, THWN-2 or XHHW-2 in conduit) So what does the * say ?

1760276293797.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,010
Location
NJ
Coming right from China. I hope I got at least 75°C lugs.
It should state the spec in the instructions or on the terminals. I wouldn't expect lower than 75c in a heater........but check.

Worst case, wire with 60c rated conductors and you're covered.
 
To avoid these ads, REGISTER NOW!
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
Looks like 9ga wire would be perfect if I could find it somewhere. I believe with 8ga wire I can use a 10ga ground. Can someone confirm.

Thanks John
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,075
Location
Fernley, Nevada, about 30 miles east of Reno.
I will be installing a 8500W heater on a 40A CB. According to this it looks like I can use #10 THHN or THWN-2. But according to Wire & Cable Your Way its only good for 30 A. So which is it?

1760276293797.png

1760276748544.png

This is table 310.60 in the code.

240.4(D) modifies this table in that it states; Small Conductors. Unless specifically permitted in 240.4(E) or 240.4(G), the overcurrent protection shall not exceed 15 amps for 14AWG, 20 amps for 12AWG and 30 amps for 10AWG copper.

240.4(E) is about tap conductors, part of this is why we can get away with using smaller wire to supply light fixtures.

240(G) is about HVAC, motors and a few others, again, allowing smaller conductors than the breaker is rated for.

As noted, the 60C or 75C column is used almost all of the time but the 90C column can be used when derating for multiple wires in a conduit.

Side note......334.80 states that the ampacity of type NM cable (Romex) is based on the 60C column.
 

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,075
Location
Fernley, Nevada, about 30 miles east of Reno.
Looks like 9ga wire would be perfect if I could find it somewhere. I believe with 8ga wire I can use a 10ga ground. Can someone confirm.

Thanks John

Table 250.122 in the code states that a #10 CU can be used as a ground for circuits up to and including 60 amps.

100 amps is #8, 200 amps is #6, 6000 amps is 800MCM.......
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
So if it says the Over Current Protection device (breaker/fuse) has a lower limit, than why publish this ????

For things like lights and receptacles you are limited with #12 to 20A and the same for 15A and 30A circuits.

There are things that does not apply to so the table is reasonable. Run a wire to an air compressor and you are not limited to the 60* ampacity.

The code is not intended to be a instruction manual...
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,010
Location
NJ
So if it says the Over Current Protection device (breaker/fuse) has a lower limit, than why publish this ????
What if it doesn't?

The installation details assume certain conditions in place. It is up to you as the installer to understand the existing hardware limitations for the branch circuit you intend to install. Vintage of the existing equipment can vary by user.
If the stars line up, then you can use a smaller conductor. If not, use a larger conductor.

Instructions "always" expect installation by a qualified electrician who knows this.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,010
Location
NJ
Ampacity derating is explained along with max ocp values permitted. Agreed, a little convoluted, but it is written well enough that it can be followed.

As stated NEC 70 is not a training manual.
Search the the web for this topic and credible sources have white papers/tech docs explaining the logic.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Looks like 9ga wire would be perfect if I could find it somewhere. I believe with 8ga wire I can use a 10ga ground. Can someone confirm.

Thanks John
you will not find 9ga wire. you need #8 THWN wire as previously stated (44a rated or higher) and yes #10 grnd is kosher. If you go with NM-b you will need #6
 