Wire confirmation for 200 ft run

wcodyd

Member
Joined
Jan 9, 2020
Messages
10
Location
Texas
I have an approximately 200’ run from my main circuit breaker to my shop. Approximately 60’ will be through a dry crawl space. I’d like to attach the cable to the floor joists in the crawl space. From the edge of the crawl space to the shop, I’ll be burying the cable in 2” conduit. I plan to have a 90 amp service to the shop. (My home has a 400 amp service entrance so there is more than enough amperage for the shop.)

I think I mistakenly purchased the wrong wire and I can’t return it. I have 250’ of 2 AWG AL XLPE SUN RES 600V TYPE USE-2 ****. It’s a 2-2-2-4 wire.

Am I correct that I can’t run wire this in the crawl space? If so, would you use a junction box on the exterior of the home, splice with Polaris connectors, and then run 2-2-2-4 mobile home feeder wire through the crawl space?

Thank you.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,267
Location
Modesto, CA
Yeah that wire cannot be ran inside

So you would need splices on both ends

MHF requires conduit indoors. I would use SER which has an outer jacket and does not require conduit
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Where did you buy the wire? Did a sales person point you to that wire and did you inform the sales person the intended use? If so you have grounds for a return.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Could you just run the conduit in the crawlspace? (Assuming the wire is OK if inside conduit...) Then out the side wall,LB,down....

Prolly the trick is getting up and into the panel, eh?
 
To avoid these ads, REGISTER NOW!

48windsor

Well-known member
Joined
Jan 24, 2013
Messages
407
Location
Olympia ,Wa.
I have to say I didnt understand some of the abbreviations .
So I researched them . Wow its easy to get lost in all of them and their meanings.
Im trying to educate myself because I too will have a long run to shop from main panel
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,267
Location
Modesto, CA
Could you just run the conduit in the crawlspace? (Assuming the wire is OK if inside conduit...) Then out the side wall,LB,down....

Prolly the trick is getting up and into the panel, eh?

If the wire is not rated or permitted for indoor use, running it in conduit will not change its insulation rating or remove the prohibition so this is inconsequential.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
(Assuming the wire is OK if inside conduit...)

If the wire is not rated or permitted for indoor use, running it in conduit will not change its insulation rating or remove the prohibition so this is inconsequential.

over the years I always get crossed up by this question... seems a perennial here, on electrician talk and over at mikeholt..

thx
 