Wire for garage heater
Colsberg2013
I have a 7500 watt garage heater. Can I use 8/2 NM-B wire? I have the wire on hand and trying to find solid is impossible?
I am assuming that's since it's already wrapped it does need to go in conduit.
Planned on running it to a junction box and then use my extra AC whip to from the junction box up to the heater.
Total run is 30ft. Thanks
Terry D
St. Louis, MO.
7500/240 = 31.25 amps x 125% = 39 amps. But look at the plate on the heater or the manual.
#8 NM-b is good for 40 amps. So you are good with that wire. Your A/C whip will have to be #8 THWN with a stranded #10 THWN ground
Use a 2-pole 40 amp breaker
NM-b does not have to be in conduit. There are some jurisdictions that will not allow it to be exposed though
C
Colsberg2013
So why would I need to have 10 gauge ground wire I'd everything else is 8ga. Just asking
Thank you
dcg9381
Austin, TX
You *really* need to read the name plate on that heater before deciding. If it's true 7500 watt continuous (39 Amps), I would not use that wire or a 40A breaker:
"NEC sizing rules. Secs. 210-22(c), 220-3(a), 220-10(b), and 384-16(c) all relate to the sizing rules for overcurrent protective devices (OCPDs). The first three all specify the same requirement: OCPD size = 100% of noncontinuous load + 125% of continuous load."
You don't want that breaker to trip after it runs for 2 hours...
sparky 1971
Central Iowa
Huh? Are you trying to say he needs a 70 amp circuit for a 7500 watt heater? (31+39). It will be just fine on a 40 amp circuit, which by the way is sized correctly. A heater is a continuous load only, not both.
mike93lx
Richmond, VA
As I read it, if the heater is a continuous 7500 watt load, he's under-sized at 40amps.
Sorry, I think that's for current protection on a feeder with multiple loads. In this case, I think the math is (39A continueous x 1.25%) = 48.75A. I'd say he needs a 50A "standard" breaker. The feeder wire needs to follow the breaker. Apparently there are breakers that are rated for 100% operation, so if he got one of those the 125% rule would not apply.
I don't want to dive too deep into the NEC on this. I'll just say this: In my experience many breakers cannot do more than 80% rated load for more than a few hours. They get hot and flip after that... This is a case that appears to be right on that line. Needs a "continuous load" beaker or needs to be sized 125%.
Check your math. 7500w / 240v = 31.25a, as already stated above. 39amps is with the 125% already applied