Wire Gauge for Motor Starter

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Back with yet another compressor wiring question - I plan on adding a starter/contactor to my compressor when I get it hooked up. I want to add a remote switch to switch the contactor on and off from the garage (compressor and starter are in another room). What gauge wire should I use for the switch? Do I have to use the same gauge wire as the motor (I'll be using 10 gauge THHN)? Since it'll have only a small amount of current to energize the coil, can it be smaller gauge? This is the starter I was going to buy: https://www.amazon.com/dp/B01MTS46KC/_encoding=UTF8?coliid=I1578QQWVCSU5&colid=38XAXG6RZ11QD
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,139
Location
Minneapolis
Tell us what kind of compressor you're talking about and the motor size, or at least provide a link to your previous question.
 

donpauli2

Well-known member
Joined
Aug 6, 2013
Messages
91
Location
central Illinois
To put a switch and use 120 volts or 240 since you're activating only the contractor coil, 14 is sufficient but not to operate the motor itself


Sent from my iPhone using Tapatalk
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
Motor Control Conductors are addressed in NEC table 430.72(B) and the breaker (or fuse) size will control the size of the control wires if tapped directly from the circuit feeding the motor.
Since the control circuit is going to extend beyond the enclosure........

If the breaker is no larger than 45Amps you can use a #14
If no larger than 60Amps you will need a #12
Up to 90 amps a #10

Edit: Since the recommended C/B size is 50 Amps, then a #12
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
To put a switch and use 120 volts or 240 since you're activating only the contractor coil, 14 is sufficient but not to operate the motor itself

1 problem is that the disconnect is required to shut off ALL conductors to the motor; even the control wires and you would need a fused control transformer or if tapped off of the main conductors, a fuse in the control circuit
 
Last edited:
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
The disconnect will shut off all conductors. I was going to simply wire the pressure switch and the remote toggle switch in series to the coil of the contactor. You're saying I'd need a fuse for that? I wouldn't have to do that if I was using just the pressure switch. I don't see how adding another switch changes that. I also don't see the need for a transformer?
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,731
Location
SE Michigan
The electrical load due to energizing the coil is milliamps usually. Good to follow the code but something like a 100va dry transformer would probably work if you ran a 120vac control voltage. And that's good for ~1 amp....
 
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I'm having a hard time understanding why I need a transformer. If I didn't have the remote switch, I'd just have the pressure switch wired directly to the coil without any transformer. All I'm doing is adding a second switch in series with the pressure switch. Why can't I just do that?

Is the transformer to bring the voltage to the coil down (the coil is rated for 240V so that's probably not it), or is it so the wiring to the remote switch is low voltage? (I'm guessing that's it) I'm already running high voltage to the compressor, so one more set of high voltage wires isn't a big deal.
 
Last edited:
To avoid these ads, REGISTER NOW!

1500hd

Well-known member
Joined
Jul 1, 2007
Messages
94
Location
Mid Michigan
You are correct, just need to wire a switch in series with the pressure switch. Most starters have L2 jumpered to A2 of the coil. Switch the L1 line from pressure switch with #14 wire.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
You don't need a fuse OR a transformer. That was in response to donpauli2's post (#4) :willy_nil
All you need is #12 (NOT #14)to the remote switch since the suggested breaker size is 50Amp
Reread post#5.
It's in the NEC
 
OP
E

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I'm actually using a 40 amp breaker per wyliesdiesels recommendation in the other thread. I suppose I can run 12 gauge anyway in case I need to upsize the breaker to 50 amps.

Most of my wiring will be in conduit, but there is a section where I will have 8/2 Romex spliced to the #10 THHN to power the compressor. I assume 12/2 Romex spliced to #12 THHN is fine for the control wiring?
 
Last edited:

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA
12/2 NM would be fine for the control wiring as long as it is protected from physical damage.
...but Quincy recommends a 50 Amp breaker in their specs!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
You don't need a fuse OR a transformer. That was in response to donpauli2's post (#4) :willy_nil
All you need is #12 (NOT #14)to the remote switch since the suggested breaker size is 50Amp
Reread post#5.
It's in the NEC

I'm actually using a 40 amp breaker per wyliesdiesels recommendation in the other thread. I suppose I can run 12 gauge anyway in case I need to upsize the breaker to 50 amps.

Most of my wiring will be in conduit, but there is a section where I will have 8/2 Romex spliced to the #10 THHN to power the compressor. I assume 12/2 Romex spliced to #12 THHN is fine for the control wiring?

12/2 NM would be fine for the control wiring as long as it is protected from physical damage.
...but Quincy recommends a 50 Amp breaker in their specs!

Where do you see 50a recommended by quincy?

The only time i see that is on the distributors site.

I searched quincy's manuals and couldnt find a recommended breaker...
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,731
Location
SE Michigan
I'm having a hard time understanding why I need a transformer.

You don't. My example of a 100va transformer was to show how low the current requirement would be.

If you do use a "wall switch" I would carefully label it inside and out, that it switches 240vac. Someone in the future will greatly appreciate that.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,584
Location
Fullerton, CA

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
You don't. My example of a 100va transformer was to show how low the current requirement would be.

If you do use a "wall switch" I would carefully label it inside and out, that it switches 240vac. Someone in the future will greatly appreciate that.

You really dont need to switch both sides of the coil. One side is sufficient.

It IS on the distributor's site under SPECS
aircompressorsdirect.com/Quincy-2V41C60VC-Air-Compressor/p855.html?gclid=CLSsqs3NndICFRNWDQod3t4J3A

Do you suppose it's the wrong info and the info that YOU gave was correct? :dunno:

I was only pointing out how the manufacturer doesnt list this in any manual that i read available on their site. I was hoping to find it somewhere...
 