Gummi Bear
Well-known member
Charles (in GA) said:I realize you probably have quite a bit of training/education at this, I have not, and don't wish to argue, just to state what I read in the code. This appears to be a change in the 2005 code from previous versions (looking at the page markings), and this may be the cause of the misunderstanding. I too would think you would want to use actual nameplate numbers for calculating values but the code state specifically otherwise (as I read it). I have omitted text in exceptions 1 and 2 that is irrelevant to the discussion. Exception No. 3 could carry the day, but I suspect that most large compressors are not "listed appliances", being built of off the shelf component pieces. Note that none of this discussion pertains to portable, plug in compressors, but rather to hardwired compressors on dedicated branch circuits.
Note that 90.5(A) defines shall as mandatory.
2005 NEC
Article 430 - Motors, Motor Circuits, and Controllers
430.6(A)(1) Table Values. Other than for motors built for low speeds (less than 1200 RPM) or high torques, and for multispeed motors, the values given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250 shall be used to determine the ampacity of conductors or ampere ratings of switches, branch-circuit short-circuit and ground-fault protection, instead of the actual current rating marked on the motor nameplate. Where a motor is marked in amperes, but not in horsepower, the horsepower rating shall be assumed to be that corresponding to the value given in Table 430.247, Table 430.248, Table 430.249, and Table 430.250, interpolated if necessary. Motors built for low speeds (less than 1200 RPM) or high torques may have higher full-load currents, and multispeed motors will have full-load current varying with speed, in which case the nameplate current ratings shall be used.
Exception No. 1: Multispeed motors …………………..
Exception No. 2: For equipment that employs a shaded pole or permanent-split capacitor-type fan or blower motor that is marked with the motor type…………
Exception No. 3: For a listed motor-operated appliance tha is marked with both motor horsepower and full-load current the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating on the appliance nameplate to determine the ampacity or rating of the disconnecting means, the branch-circuit conductors, the controller, the branch-circuit short-circuit and ground-fault protection and any separate overload protection.
You are correct. For a motor that is loose, or a part of a non UL (or other listing agency) appliance (machine, pump, conveyor or whatever) you do use the NEC Tables.
It's that listed part that is a source of confusion sometimes. What that's telling us, as the end installer, is that the machine has been engineered, and that these values given on the nameplate are what is necessary. Kind of a 'stamp of approval' if you will.
Good reference.