I am not exactly what you are talking about, but the last server room I worked in, all of the computer outlet used isolated ground receptacle (IGR) (orange).Yeah, for $100 or so more seems like I shouldthe electronics/servers def. seem to need the neutral based onwhat I read, some weird data loss, boot problems, etc, if not sized right.
Care to elaborate why these aren't good? (other than cost, ha).
And, would you go with a different SubPanel then? Or just go with this one since it's the size I'd like, and just not use the Plug-On Neutral CBs.
I am not exactly what you are talking about, but the last server room I worked in, all of the computer outlet used isolated ground receptacle (IGR) (orange).
Someone correct me if I am wrong, but as I recall, IGRs required a separated, INSULATED (green) ground wire from the actual receptacle, un-broken, un-spliced all the way back to the ground bar in the load center. The ground pin is ISOLATED from the frame of the receptacle and the box that the receptacle is mounted in.
http://www.homedepot.com/p/Siemens-...PIPHorizontal1_rr-_-206602485-_-207158494-_-N
may be more suited for my need if I go Siemens.
Care to elaborate why these aren't good? (other than cost, ha).
And, would you go with a different SubPanel then? Or just go with this one since it's the size I'd like, and just not use the Plug-On Neutral CBs.
I am not exactly what you are talking about, but the last server room I worked in, all of the computer outlet used isolated ground receptacle (IGR) (orange).
Someone correct me if I am wrong, but as I recall, IGRs required a separated, INSULATED (green) ground wire from the actual receptacle, un-broken, un-spliced all the way back to the ground bar in the load center. The ground pin is ISOLATED from the frame of the receptacle and the box that the receptacle is mounted in.
["Leaning toward the Square D QO with the PLug On Neutral... stupid expensive breakers but less work, less hassle to be safer.
Model: QO154M200PC
54 Space / 54 Circuit
39.4" Tall -- Seems to be a good size / space between 40 and 60 space.
https://www.amazon.com/dp/B00KHVLZVU/?tag=atomicindus08-20
Opinions? I don't see copper in the picture but it says it's copper ??
Can this be surface mounted"
plug on neutrals only save work if you are using gfci or afci breakers. they don't save any work if you are using regular breakers. this panel is surface or flush mount
Quick question here: Are Square D QO PON Panels able to use standard QO (NON-PON) breakers in them? I'll be installing a panel in my garage in the future, and I have always used Square D QO's. Just wanted to clarify that the PON panels are compatible with standard QO breakers. Thanks for any info!![]()
To wrap this up..
3/0 hot wires (2)
3/0 white neutral wire
#4 green wire going (2) 1 each to a ground electrode
#6 green wire back to main panel ground
For the ground electrode at the shop / sub-panel. I currently have only 1, and it' sticking up about 2'. My understanding is I would want to get this down to flush / near flush with ground, and install 2 of them approx 8' apart, is there any reason to do additional or put 1 on opposite side of building, or could I put both at back of building? Right now they're kind of in the way on the side I work/use.
wire to rods max size is #6. Use bare solid copper #6.
EGC going back to main panel can be #6 for 200a. to be code compliant it must be green insulated.
rod should be pounded flush.
unless u can prove 25ohms or less resistance to earth, to be code compliant 2 are required. space min 6' apart.
http://www.buildmyowncabin.com/nec/nec2014_table250.66.html
Where are you getting #6 for the rod wire size? Everything I'm finding is #4 when using 3/0, and #6 ground back to main panel.
To wrap this up..
3/0 hot wires (2)
3/0 white neutral wire
#4 green wire going (2) 1 each to a ground electrode
#6 green wire back to main panel ground
For the ground electrode at the shop / sub-panel. I currently have only 1, and it' sticking up about 2'. My understanding is I would want to get this down to flush / near flush with ground, and install 2 of them approx 8' apart, is there any reason to do additional or put 1 on opposite side of building, or could I put both at back of building? Right now they're kind of in the way on the side I work/use.
qo is more of a commercial type product. you can order them with push in or bolt on breakers.
I got one of these last year, but never installed it on my main panel on the house:
https://www.amazon.com/dp/B00CONA1OQ/?tag=atomicindus08-20
Should I run 1 on the house or 1 on the shop or both? Worth it or snake oil and hassle to deal with?
Also, looks like my main panel on the house won't let me install a 200A CB so I'm going to have to double-up the main lugs and run a fused disconnect there next to the main panel.
Which do I want?Prices from $100ish to almost $500!! YIKES
http://www.homedepot.com/p/Eaton-20...General-Duty-Safety-Switch-DG224NRK/202275985
https://www.amazon.com/dp/B0052MFWM2/?tag=atomicindus08-20
https://www.lowes.com/pd/Eaton-Type-BR-200-Amp-2-Pole-Circuit-Breaker/3047900
https://www.amazon.com/dp/B00PSN6FQM/?tag=atomicindus08-20
What do u mean by double up the main lugs?
Do u mean u need dual lugs so u can feed two 200a loads off of one original set of lugs or wire?
None of those disconnects have dual load side lugs.
Most of us electricians who were also computer/network techs thought it was overkill but werent complaining since it was tons of work.
I sent you a priavet PM of my setup as i prefer to keep it private, but I don't know if you got it or not.
@wyliesdiesels, I know you probably know this, just more for general FYI I posted this more because recently has become dear to my heart.
It's funny that I came across this post. I was the tech guy trying to explain the "over kill". I now mange the Point of Sale for quick service. We have right at 2000 terminals. I have not had to mess with quality of electrical supply since the 80's. I am sure a lot has changed. But because of the recent issues, I'm back....
I never heard of running two grounds. Most conduit in those days was metal. Some even supplied the ground (ie no ground wire), but they all (grounds) were bonded together. The IG isolated the ground lug from the parts that could come in contact with the metal box.
We required a separate circuit back to the building ground. It had to have it's own Hot, neutral, and ground. If the outlet was not IG, then the ground could be" whatever the conduit was, depending on circumstances.
Most of the neutral sizing had to do with the feed for it's phases.
Here is a snippet from this artical oversizing neutral wiring
In modern facilities the neutral wring should always be specified to be the same capacity as the power wiring (or larger). This is in contrast to the electrical codes which may permit undersizing the neutral wire. An appropriate design in the case of a large Personal Computer load like a call center is to specify the neutral wiring to exceed the phase wire capacity by about 50%. Particular attention should be paid to wiring in office cubicles. This protects the building wiring, but does not help protect the transformers.
Back in the day when loads tended to be resistive, for the same amp draw on different phases on the same neutral would tend to cancel each other out. So when one phase hot was more positive and it's neutral was more negative. Then the other hot would be more negative and the neutral would be more positive. The negative and positives tending to cancel each other out as long as the load (amps) were the same. When computers came along with the switching power supply, that mess things up. You would go from full power to nothing several times a second. So the neutral could not count on that balance, hence the harmonics.
All this maybe more than you care, just I am having to get more involved in some issues and it just made some old brain cells fire.![]()