I am doing my wiring now and I am locating my compressor about 50 feet from the panel. it will be a 220 volt 5 horsepower unit (don't know which one yet) is 10-3 wire big enough?

So what about the start up draw ? I know we have been through this many times but ,
Not sure on the 28 amp 5 hp motor but my 7.5hp motor is at 33 running amp and the start up draw is around 76 amps ! Thus the reason i installed a #4 wire on mine and an 80 amp breaker.
I would think for the 5hp unit i would run at least # 6-2 wire and a 60 amp breaker. The compressor will work on less but we know what happens with lack of wire on electric motors ..............![]()
You should be able to up the breaker size WITHOUT upping the wire size if in fact you are having nuisance tripping. You shouldn't need #6 for a 5hp unit unless the motor is far away from the panel.
BTW ,
I wouldnt put an oversized breaker on an undersized wire, Dont think thats a good idea.
*****************************************
If you elect to install a subpanel at the compressor (other circuits in this area could be handy) you also would need to carry a neutral to the subpanel.
It's allowed, by code, for certain things like a compressor on a dedicated circuit.
) The start-up spike doesn't last long enough to over heat the wire, thats why you don't have to size the wire for the spike.
The code does allow for a larger size breaker:
Table 430.52
Maximum Rating or Setting of Motor Branch-Circuit Short-Circuit and Ground-Fault Protective Devices
Single-phase motors- "Inverse Time Breaker" 250% of full load current
28amps X 2.5= 70 amp breaker maximum
Mark
What he said.The start-up spike doesn't last long enough to over heat the wire, thats why you don't have to size the wire for the spike.
The code does allow for a larger size breaker:
Table 430.52
Maximum Rating or Setting of Motor Branch-Circuit Short-Circuit and Ground-Fault Protective Devices
Single-phase motors- "Inverse Time Breaker" 250% of full load current
28amps X 2.5= 70 amp breaker maximum
Mark
Remember, the breakers and the wire is not going to go up in smoke if you go over the normal specs for a short period of time. There is a lot of safety built into the components.
Maybe if the run of wire was very short, would the price differential be neglible. All I know is with the price of copper and the lengths I would need, bumping up to the next size wire wouldn't be worth it.
Maybe if someone has the code listing for the amount of A a wire can take for a short period of time...I know I've seen the chart before. Might make it a little easier to see/understand.
Here you go:
#12 wire = 20 amp breaker 16 amp load max
# 10 wire =30 amp breaker 24 amp load max
# 8 wire = 50 amp breaker 40 amp load max
# 6 wire = 60 amp breaker 48 amp load max
Matt Murphy