20 HP compressor with twin 10HP motors that start sequentially. It is about 75' from the breaker panel. I plan to wire in a disconnect outside where the compressor is.

I have 120/208 Wye service. Will be running these motors at ~208V.

What size wire will I need?

See pics:
 

Attachments

  • IMG_5387.jpg
    IMG_5387.jpg
    100.2 KB · Views: 148
  • IMG_5388.jpg
    IMG_5388.jpg
    113.7 KB · Views: 152
  • IMG_5389.jpg
    IMG_5389.jpg
    103.7 KB · Views: 100
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I'm not sure you'd be able to use that GE motor, since it doesn't appear to be rated for 208V. But assuming you could use it, I think you'd need wire with an ampacity of 70A, which means #4 copper wire (table 310.16).

How I arrived at that answer:
According to 430.24, you need to take 125% of the FLC of the biggest motor, and 100% of the FLC of all of the smaller motors and add them all up to get the total ampacity required. To find the FLC, you look it up in table 430.250. A 10 HP motor at 208V 3 phase has an FLC of 30.8 amps.

Since both motors are 10 HP, they should both have an FLC of 30.8A. 125% of 30.8 is 38.5A. 38.5 + 30.8 = 69.3A. Round it up to 70A.

Someone correct me if I'm wrong.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Hmm I wonder if the internal jumper wiring for the GE motor is different for 208 than for 230, Ill have to pull the cover and check.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Units like that leave the factory designed for a specific voltage. The motor only being one piece of the puzzle.

Have you verifed the starters, coil voltages, overload settings, internal wiring, terminal blocks, etc are all appropriate for operation at 208v?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
I'm not sure you'd be able to use that GE motor, since it doesn't appear to be rated for 208V. But assuming you could use it, I think you'd need wire with an ampacity of 70A, which means #4 copper wire (table 310.16).

How I arrived at that answer:
According to 430.24, you need to take 125% of the FLC of the biggest motor, and 100% of the FLC of all of the smaller motors and add them all up to get the total ampacity required. To find the FLC, you look it up in table 430.250. A 10 HP motor at 208V 3 phase has an FLC of 30.8 amps.

Since both motors are 10 HP, they should both have an FLC of 30.8A. 125% of 30.8 is 38.5A. 38.5 + 30.8 = 69.3A. Round it up to 70A.

Someone correct me if I'm wrong.

Huh?

It clearly says 208-230/460 on the nameplate...
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Units like that leave the factory designed for a specific voltage. The motor only being one piece of the puzzle.

Have you verifed the starters, coil voltages, overload settings, internal wiring, terminal blocks, etc are all appropriate for operation at 208v?

Sure haven't I just got it set. I'm used to wiring multi tap motors but thats about the extent of my experience. Can you give me some 101 on what to look for on these?

I did briefly run both motors at separate times on 208V to make sure it functioned, but I need to really shake it down to make sure I don't damage anything that isn't setup right.

So consensus is 4/3 huh. Ill probably see if I can get that in romex I'm sure its $5/ft...
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,726
Location
SE Michigan
Your easiest clue on what-voltage the unit was formerly wired at is how the motors are configured.

If 4-5-6 are jumpered together then was on low voltage (208/240).

If you have L1-1, L2-2, L3-3 then was on high voltage.

You can normally read the coil voltage on the contactors themselves. It might have a control transformer instead of sending 240/480vac thru the pressure switch. In that case the transformer likely has a jumper configuration like the motors.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Your easiest clue on what-voltage the unit was formerly wired at is how the motors are configured.

If 4-5-6 are jumpered together then was on low voltage (208/240).

If you have L1-1, L2-2, L3-3 then was on high voltage.

You can normally read the coil voltage on the contactors themselves. It might have a control transformer instead of sending 240/480vac thru the pressure switch. In that case the transformer likely has a jumper configuration like the motors.

Thanks, I wired them to low voltage to test them but didn't look at the other odds and ends.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
Why bother with Romex?

Get some EMT, black #4 THHN and 3 rolls of tape- red blue and green.

Can you post pics of the starter box with cover on and off as wel as a close up of the contactors and the overload relay block?

In addition to a possible coil change, You may need different overload heaters or if solid state, an adjustment to the setting.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Why bother with Romex?

Get some EMT, black #4 THHN and 3 rolls of tape- red blue and green.

Can you post pics of the starter box with cover on and off as wel as a close up of the contactors and the overload relay block?

In addition to a possible coil change, You may need different overload heaters or if solid state, an adjustment to the setting.

Yeah I will be able to get some shots friday or Saturday and post them.

What size EMT you think I will need for that run?
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
Huh?

It clearly says 208-230/460 on the nameplate...

I wouldn't say it CLEARLY says 208v. It says 230/460 on the left side. I had to zoom in a lot, and even then I could barely make out where it says compatible with 208v.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
70-100A circuits only need a #8 Cu ground wire except it's got to have green insulation, or stripped for it's entire visible length (not in the conduit)

Ok ground size was my next question. What size conduit fits 3 - #4s and 1 - #8? 1”?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,519
Location
Richmond, VA
If you want to save some money, use #2 AL XHHW

1" emt will still work if you don't run a ground, but if it is a complex run, stepping up a size would probably be worth it
 
To avoid these ads, REGISTER NOW!
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Also, is your POCO good with two 10hp motors? If this isn't industrial service, it might be a problem

They better be. I gave them a list of all the equipment I have when I built this place. I have 400 amp service.

They pulled 500KCM wire for my service ~ 375'.
See Pic.
 

Attachments

  • IMG_4158.jpg
    IMG_4158.jpg
    126.6 KB · Views: 85
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,519
Location
Richmond, VA
They better be. I gave them a list of all the equipment I have when I built this place. I have 400 amp service.

They pulled 500KCM wire for my service ~ 375'.
See Pic.

It isn't about wire size, it's the transformers.

In residential service, 10hp is generally a no go, from what I have read here
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
It isn't about wire size, it's the transformers.

In residential service, 10hp is generally a no go, from what I have read here

I can take a pic of the transformers, but they had to set a new pole and 3 large transformers off the highway for my service. From the load sheet I turned in I would hope they got this right.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
For my disconnect I will go with a GE outdoor non fused to match other I have around the shop, however I see I can get a 20HP rated disconnect, but it only has a 30 amp rating. I am expecting to run a 70 amp breaker at the panel and pull more than 30 amps should I upsize this? Or is it rated differently since we are dealing with motors?
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Ok I got the wire ran and all that finished up, however I took some pics of the wiring inside the panel at the compressor since it looks like a lot of the components were setup at 460V. My service now is 208V.

It looks like the control transformer I can rewire for ~240 volts. I am assuming this will work with 208V?

The rating on the contactors shows they are only good for 7.5hp at 208V so I am assuming I will need to upgrade these? Any good places to source this?

The overload relays appear to max out at ~16 amps. I will need something closer to 30 amps going to 208V. Where can I source these?

Also the relay in the center... Not sure whats going on with that.

Also the leads going to the motor are 12 awg. This was probably fine for 460V. Will I need to rewire these to 10 awg for the increased amperage on 208v?

Here are the pics:
attachment.php


attachment.php


attachment.php


attachment.php


attachment.php


attachment.php
 

Attachments

  • IMG_5412.jpg
    IMG_5412.jpg
    88.6 KB · Views: 191
  • IMG_5408.jpg
    IMG_5408.jpg
    88.7 KB · Views: 191
  • IMG_5404.jpg
    IMG_5404.jpg
    121.8 KB · Views: 192
  • IMG_5403.jpg
    IMG_5403.jpg
    114.4 KB · Views: 187
  • IMG_5401.jpg
    IMG_5401.jpg
    148.5 KB · Views: 195
  • IMG_5413.jpg
    IMG_5413.jpg
    111.6 KB · Views: 188

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
however I see I can get a 20HP rated disconnect, but it only has a 30 amp rating.
Huh?:headscrat :confused:
I noticed also you didn't list your location on your profile (everyone else on this thread has)
Different PoCos have different rules re: max hp they'll allow on their system.
For instance So Cal Edison's rule is a 10HP max on resi services
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
Huh?:headscrat :confused:
I noticed also you didn't list your location on your profile (everyone else on this thread has)
Different PoCos have different rules re: max hp they'll allow on their system.
For instance So Cal Edison's rule is a 10HP max on resi services

I am in South Louisiana and no residential service here.

I was able to find a disconnect with the correct ratings.

Update on the controls I posted pics of earlier. I called klockner-moeller and the parts guys were helpful with crossing over all the part #'s to versions that will work with the higher amperage at 208V. However its nearly $500 so I am currently looking on ebay for some better pricing.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
I wouldnt run the control transformer 240v windings on 208v. the 120v output might be too low for the contactor coil and thus cause chattering.

Get a transformer rated for 208v or better yet, since you need a new contactor anyways, just get one with a 208v rated coil and bypass the control transformer all together.

have you asked your PoCo about max HP limits on their system?

The in-rush current on larger motors can be very high...
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,721
Location
NW Iowa
For my disconnect I will go with a GE outdoor non fused to match other I have around the shop, however I see I can get a 20HP rated disconnect, but it only has a 30 amp rating. I am expecting to run a 70 amp breaker at the panel and pull more than 30 amps should I upsize this? Or is it rated differently since we are dealing with motors?

I think a 30 is good for 20hp on 600v 3 phase. You have 208 so it will probably take a 100A disconnect.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,721
Location
NW Iowa
I wouldnt run the control transformer 240v windings on 208v. the 120v output might be too low for the contactor coil and thus cause chattering.

Get a transformer rated for 208v or better yet, since you need a new contactor anyways, just get one with a 208v rated coil and bypass the control transformer all together.

Kind of agree with just getting 208 coils. That cabinet is pretty messy as it bigger starters aren't going to help.

If you go to eBay stick with name brands. Used NEMA or new IEC are both fine for your purpose.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,721
Location
NW Iowa
He's been asked this several times and deflected or ignored it. I'm guessing he doesn't want the real answer.

I'm not sure why anyone thinks this is residential. He has 3 phase. I doubt this is in his back garage.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
Kind of agree with just getting 208 coils. That cabinet is pretty messy as it bigger starters aren't going to help.

If you go to eBay stick with name brands. Used NEMA or new IEC are both fine for your purpose.

With the control transformers means the controls are 120V, but the OP would either need to get control transformers that have a 208V primary, or supply a 120V control circuit, I would not try to change it. Since the OEM starters are IEC type, I would not try to fit considerably physically larger NEMA style starters in their place even though I personally prefer NEMA over IEC, but do have to agree with sticking with name brand starters, A-B is preferred by me just because have had pretty good luck with them, and will be easy to get accessories for them.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,721
Location
NW Iowa
You could just bring a neutral to the cabinet from the breaker panel. Get power from one of the line wires on the starter. If you use a small control fuse the neutral could be #14.

Keeps everything 120v and no need for a separate control power breaker.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,011
Location
Modesto, CA
I'm not sure why anyone thinks this is residential. He has 3 phase. I doubt this is in his back garage.

I wasnt thinking it was resi. But I have seen limits on HP for small 3-phase service.

Especially for end of line runs or where the PoCo installed an undersized trany for the service and the cutouts arent rated very high.
 
OP
E

EasyE

Well-known member
Joined
Dec 3, 2011
Messages
72
I wouldnt run the control transformer 240v windings on 208v. the 120v output might be too low for the contactor coil and thus cause chattering.

Get a transformer rated for 208v or better yet, since you need a new contactor anyways, just get one with a 208v rated coil and bypass the control transformer all together.

have you asked your PoCo about max HP limits on their system?

The in-rush current on larger motors can be very high...

Good thought on the 208 contactor I will take a look and see what I can find.

As for the poco requirements on motor size. I built this shop and sent the power company a build sheet of all the equipment I would be running. They came out and set a new pole and hung 3 transformers for the service based on my build sheet. I would think they would have seen the numerous motors and machine tools and sized them accordingly. I am in an industrial area so I don't think I would call that the end of the line. My shop has 400 amp service, I would be surprised if motor start up exceeds 200 amps.

As for controls I am looking at moeller - eaton stuff so should be decent quality I would think.
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,837
Nobody else has mentioned this, but make sure your motor rotations are correct before you put belts on and connect the whole thing. I would hate to see what mess two 10 hp motors would make if they were turning the wrong directions or what amps they would pull. Just a word or warning as even the experienced electricians will sometimes forget this and have something burn up or run without oil pressure from reverse rotation.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I doubt 2 10's are a problem, they set it knowing he has 400 and a reason for 3 ph. I have 400 single, ****** is a 15. I have small motors, biggest is 5, no flutter from it. I got with engineering before they set this, got a big fat wire from the ******, got it in writing to spec it.
Had a resident hook up the other day, poco used the same wire that was on a 60 to feed new 200, really looked strange,, ha. 4 to 4/0.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
As for checking, I was at a job a while back, the installer didn't bother checking voltage, they were still ting to sort out who's fault it was, spose to be 230, was 480. . They didn't want to pay to have supervision,,, how hard can it be,,, what could go wrong? Had another one not too long ago, didn't want to pay the 2 g to manage it,,, 25 later,, ha.
 