Wire size for mini-split

minerfarmer

Well-known member
Joined
Feb 11, 2012
Messages
104
Location
Central Illinois
I bought a used Mitsubishi (MUZ-GE18na). I have lined up a local HYVAC guy to charge the system. The installation manual I got online seems to say to use 14 gauge wire on a 220volt breaker. Can I use 12/2 with ground on a 15 amp 220 volt breaker to run this unit or am I missing something?
 

Attachments

  • image.jpg
    image.jpg
    133.7 KB · Views: 45
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
You can use 14/2 & a 15A 2 pole breaker if you wish, as it's already had the 125% done by the manufacturer. But as a side note I don't like 14 AWG for anything except residential lighting & control wiring, so 12/2 is fine. BTW "220" is not a domestic voltage unless your in the 50 hertz world like Europe, China, Africa, for many decades it's been either 208 or 240 volts.
 
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
You can, and I recommend, running this circuit with 12 gauge instead of 14. The 14 can flow "up to" 15 amps and the 12 gauge "up to" 20 amps. There is no penalty for upsizing the wire and it will allow you to upsize the breaker in the event that you desire a larger heat pump in the future.
 