wire size for pump motor/house

sherrod624

Well-known member
Joined
Apr 28, 2013
Messages
110
Location
Sims, NC
I need to wire a 240v 1hp well motor that is 180 ft away from my house. I would also like to have a 120v light and receptacle in the pump house. From what I've gathered I can run the pump off of #12 cu. what would be the best code approved way to get the 120v for the light and receptacle? I was thinking run 12-3uf to a 6throw main lug panel like this

http://www.homedepot.com/p/Square-D...oad-Center-with-Cover-HOM612L100SCP/100190554

but surely I wouldn't feed it with a #12 feeder from 180 ft away

the pump used to be wired up to another structure that is now gone. it was wired to a 30amp breaker before. im not sure but I don't think this is correct.

any help on what is the best way to do this would be greatly appreciated

thanks
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It could be wired to 30A but 12 is too small at that distance especially for an outlet. For just the pump it probably would work fine. You should have a 10 if the wire is to serve them both and what are you going to put on the outlet. For a simple tool use its not a deal especially if its not being used at the same time,,, electric heater is another matter. Since you are adding a panel number 6 alum would be ideal and probably cheaper than 10 cu as well as give plenty/better service.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,050
Location
Modesto, CA
Doing the voltage drop calcs, #12 is fine for the FLC rating of 8a on a 1HP motor.

However, in-rush current may cause excessive voltage drop so u could use 10/3 UF-b to be sure. And if u plan to use the outlet for power tools u should go with #10

I assume the pump has a starter. The overload protection would be in that.

20a would be fine for the feeding breaker.

And motor circuits can have breaker ratings that are higher than the wire ampacity rating.
 