Hey. Nothing against your post. My brain just wanted to see it written out in black and white with what I already purchased.Was there something unclear in my post right above yours?
Hey. Nothing against your post. My brain just wanted to see it written out in black and white with what I already purchased.Was there something unclear in my post right above yours?
All good, just checking. This comes up a lot, so I think I've typed basically the same thing many times and it seems like it doesn't stick very well. Wondering if I need to approach it differentlyHey. Nothing against your post. My brain just wanted to see it written out in black and white with what I already purchased.
You sure it's 30 amp?Yeah, I don’t ever see my self pushing that limit. Biggest one time hit I have now is a 2 post car lift which requires 30A. I might look into 2/0 then. Thank you
To be fair, he's quoting breaker sizing, not running currentYou sure it's 30 amp?
Most hoists are ~2 hp, which is under 10 amps.
According to Bendpaks website they recommend a 30A breakerYou sure it's 30 amp?
Most hoists are ~2 hp, which is under 10 amps.
That does NOT mean the FLA on the motor is 30a. Breakers for motors need to be oversized to prevent nuissance tripping from in-rush current.According to Bendpaks website they recommend a 30A breaker
What size circuit breaker does a lift's power unit require?
We recommend a 30 amp breaker for your car lift.
Makes sense. Thank youThat does NOT mean the FLA on the motor is 30a. Breakers for motors need to be oversized to prevent nuissance tripping from in-rush current.
A 5HP motor has an FLA of around 23a and a 7.5HP is closer to 30a
your lift motor is probably around 2Hp
Sure, but that's not a 30 amp draw. If starting amperage was used for everything,houses would probably need 300 or 400 amp service.According to Bendpaks website they recommend a 30A breaker
What size circuit breaker does a lift's power unit require?
We recommend a 30 amp breaker for your car lift.
Actually startup currents are 4x-8x FLA so the draw would be a lot higher tham the breaker rating but its only for 100ms or so and the breaker doesnt trip with such a short spike in current.Sure, but that's not a 30 amp draw. If starting amperage was used for everything,houses would probably need 300 or 400 amp service.
Likely they recommend that to avoid any nuisance trips as the momentary starting draw is probably near that.
Still seems high, but that's just my 2 cents. 3hp is around 10 amps. A 20 amp breaker shouldn't trip.
Is there a thing as too much power?? Wouldn't you kick yourself in the **** if you outgrew your power supply someday?? Some things to think about. I called my power company when I ran the power out to my shop and they were more than happy to come out to my house and talk everything over and tell me exactly what I needed to purchase.