Where are u located?

4/0 use to be allowed for 200a service but the chart allowing that has been removed in the 2014 NEC.
 

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
YOur local power company/coop may have specs, in spite of no enforcement, etc. Ours does. They even spec the conduit and sweeps and ground requirements. If it is not to their specs, they just go away to the next job.

worth a check with them..
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Rural Missouri...No codes enforced or inspections

Regardless, u should still follow code so u dont have any issues.

YOur local power company/coop may have specs, in spite of no enforcement, etc. Ours does. They even spec the conduit and sweeps and ground requirements. If it is not to their specs, they just go away to the next job.

worth a check with them..

That only applies on the line side of the meter for underground services. PoCo has different rules than the NEC.

Overhead service entrance and Load side of meter is governed by the NEC.

It's still basically the same thing. Not sure why they changed it to the 83% thing.

Yes now they just require load calcs but base it on the same 83%. Why did the code panels even need to change it? Stupid IMO
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Only reason that I can think of is it makes it harder to misuse it, because have do the calculations instead of going to a table. Just a WAG on my part.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That wire is okay for 200A service but technically it has to be terminated outside because it's URD with only a USE-2 rating which is not a fire resistant insulation. You'd need to switch to SER for any interior run to the breaker panel. You can do this by using an exterior main disconnect.
 

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
Installing 200amp service from dual tap meter on pole to garage. I have conduit laid. Distance is about 125ft. What size wire is required. I will be using ground rod also at shop

Will this wire work for me
http://www.lowes.com/pd/4-0-Aluminum-Urd-Service-Entrance-Cable-By-the-Foot/3127531


Thanks for the help

You said this will run from your dual tap meter, is there any over current protection there? if not, you might want to consider it, and if you do, the wire you use will need to be 4 conductor
 