Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
Menards has big sale going on now. What size wire do I need for a 200 amp run from house to shop? Over 200 foot. Running off a 100 amp breaker until I get new service. Might not be for years. Just want big enough for the day o do decide
 
To avoid these ads, REGISTER NOW!
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
Ran 60late are old one with no problem. Going to have 100i here and may never upgrade to 200. Welders and compressor. But they don't run at the same time though
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Point is, there is a BIG price difference in the wire, and terminating wire rated for 200A in 100A equipment WILL prove challenging.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Since this is on a residential property most inspectors will allow #2al or #4cu.
If not then either #1 or 1/0al, or #3 or #2cu, depending on the setting an cable/conductors used.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
If inspectors are allowing that they should be fired.

The correct answer without regard to Vdrop is #2 Cu NMB or perhaps #3 THHN (although I question this in most settings).
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
No, no on the nmb. Can't run that in conduit underground. Just throwing the nmb out there for generic info. Thhn/Thwn in conduit or some other option rated for wet.
 

IONH

Well-known member
Joined
Feb 12, 2010
Messages
2,043
Location
Central Massachusetts
Good point. Mt house has 150 service. I have a new 100amp box from a previous plan at old house
to what size for 100 tthen

Just because you have a 100 amp spare breaker box available doesn't mean you have to run 100 amp to it. Replace the main breaker with a 60 amp or whatever is equivalent size wire you ran to it. Don't forget to properly size the feeder breaker in the main panel.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Would you elaborate?





May I ask WHY you would question this? It is code correct.

Yes, the garage feeder does not carry 100 percent of the diversified load of the service, thus it is ineligible for special treatment aka undersized wires.

Not so sure. It depends on the temperature rating of the devices it connects. Section 110.14(c). It would only be valid for 75 degree terminals. 2 cu would be required for 100 amps for 60 degree terminals.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
when using bigger wire and a smaller breaker (60a breaker on #2 wire or whatever) you have to keep an eye on the size of the EGC as it must be proportionally increased when compared to the other conductors, and at some ampacities and wire size combinations, it doesnt calculate out correctly.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Yes, the garage feeder does not carry 100 percent of the diversified load of the service, thus it is ineligible for special treatment aka undersized wires.
Regardless, many inspectors DO still allow this for residential sub-panels.
In my area, #2AL is the norm for 100A sub-panels.



Not so sure. It depends on the temperature rating of the devices it connects. Section 110.14(c). It would only be valid for 75 degree terminals. 2 cu would be required for 100 amps for 60 degree terminals.
Hence my statement about it being code correct.
 
To avoid these ads, REGISTER NOW!

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Regardless, many inspectors DO still allow this for residential sub-panels.
In my area, #2AL is the norm for 100A sub-panels.



Hence my statement about it being code correct.

I wouldn't go by what some uneducated inspector allowed when you knew it was wrong. The NEC is the standard, not what some inspector allows because they are incompetent or mistaken.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I wouldn't go by what some uneducated inspector allowed when you knew it was wrong. The NEC is the standard, not what some inspector allows because they are incompetent or mistaken.
Actually our inspectors are some of the smartest around. We do not have all-in-one inspectors here who need to cover every trade. We use third party electrical-ONLY inspectors.

And it is/was NOT entirely wrong. MANY areas used 310.15(B)(6) for both sub-panels and services. It is all in the interpretation.
Because they allow us to use a 100A feeder breaker instead of a 90 that makes then "incompetent" and "uneducated"?? Come on now.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Aren't you the one always posting how dangerous electrical is and how only licensed electricians should play with it and all this - no doubt because you are a licensed electrician. And, then you come up with this? Clear code violations are acceptable because it's just a little violation? The comments to the relevant section of the 2008 NEC make it absolutely incorrect to do what your great inspectors allow. There is no matter of interpretation.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
I disagree.


an inspector does not have the legal authority to make code interpretations or exceptions. The Building Official must do it, that is whoever is in charge of the building dept and it must be written to be legal. An inspector allowing or missing a violation does not make the installation legal.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
And it is/was NOT entirely wrong. MANY areas used 310.15(B)(6) for both sub-panels and services. It is all in the interpretation.

Because they allow us to use a 100A feeder breaker instead of a 90 that makes then "incompetent" and "uneducated"?? Come on now.

310.15(B)(6) is not open to interpretation. The feeder either carries the entire load of a single dwelling unit or it does not. Its black and white.

If an inspector allows you to undersize a feeder, i would consider that incompetent. If the inspector worked with the local building official to grant you an exemption for your undersized feeder, I would consider that inspector to be a professional.

I have a feeling your 3rd party inspectors just dont care as they have no vested interest in the legality of the work they inspect. They (I am making an assumption here) get paid per inspection and want to get through their stops for the day.

Here is what happens when you have such an inspector covering the structural on a component of one of the most expensive private construction projects in the country http://en.wikipedia.org/wiki/The_Harmon
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
You disagree@! Based on what? Support your unsupportable position to show how much you know as a licensed electrician.
Based on the fact that this is NOT as black and white as you think it is. MANY areas are/were the same as mine with regard to this.
I know quite a bit as a licensed electrician, but you can attempt to discredit me all you want. I don't have to prove myself to the likes of you.

mrb & mark, you're right . I am wrong. That's what you want to hear so there it is, patronizing as it is. :thumbup:
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
I just want a cite to the language of a section of the NEC to show that this is a matter of interpretation and that it is not as black and white as I think it is.


What's the deal on dual marked breakers termination rating wise: I see every breaker is marked 60/75 - what does this mean? Does it default to 60 when installed in a panelboard with other breakers?
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
My understanding is breakers are marked as 60/75 simply to make it clear that it’s okay to use either a 60 or 75 degree rated wire connected to the breaker.

I just want a cite to the language of a section of the NEC to show that this is a matter of interpretation and that it is not as black and white as I think it is.


What's the deal on dual marked breakers termination rating wise: I see every breaker is marked 60/75 - what does this mean? Does it default to 60 when installed in a panelboard with other breakers?
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
My understanding is breakers are marked as 60/75 simply to make it clear that it’s okay to use either a 60 or 75 degree rated wire connected to the breaker.

I seem to remember discussion that whenever a dual marked breaker is put in a panel with any other breakers that it defaults to 60 degree termination. Therefore, for 100 amps or less you basically always have to use the 60 degree column.

Isn't this correct?

Also, in looking at the QO breaker I see a 40 degree marking on the breaker. What is this referring to?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I can't say you're wrong, but I can't find any info that says you're right. Scanning through the NEC I don't see anything that supports your memory. That would mean if I pulled a bunch of circuits using conduit with THHN (75C) wire and had one circuit that used NM (60C) I would have to use the 60C degree rating for sizing all of the circuits. That doesn't seem right to me.

I seem to remember discussion that whenever a dual marked breaker is put in a panel with any other breakers that it defaults to 60 degree termination. Therefore, for 100 amps or less you basically always have to use the 60 degree column.

Isn't this correct?

Also, in looking at the QO breaker I see a 40 degree marking on the breaker. What is this referring to?
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
the 40deg marking is the ambient operating temperature. the 60/75 is the terminal temperature rating, meaning it may be used for wire of the appropriate type and sized based on those ratings consistent with the nec requirements.
 
OP
D

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
I will be running a 100 amp breaker off house panel. From previous experience I had to trim some of the strand to fit the wire into the breaker. Is this allowed?
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
the 40deg marking is the ambient operating temperature. the 60/75 is the terminal temperature rating, meaning it may be used for wire of the appropriate type and sized based on those ratings consistent with the nec requirements.

But what about my question on the 60/75 dual marked breakers defaulting to 60 when put in a panel with other dual marked breakers? Do you have any understanding of that situation?

There was a discussion here where some very good members PHR and Charles in Georgia stated that you had to use the 60 degree rating with these dual marked breakers.
 