Wire size

Monkey Radio

Well-known member
Joined
May 31, 2011
Messages
74
Location
Normandy Park WA
Looking for wire size for a 100 amp sub panel. The run will be about 250-300 ft. I have been told several sizes like #4, #3, #1 copper. Or increase the size and run aluminum. Sure would like to no what is the right size to use for voltage drop. Next question is there a standard height for wall outlets. Mainly for the work bench.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
General rule is no more than 3% voltage drop. Based on a calculator I have you'd need to use a minimum of #1/0 copper for 300'. 250' you can squeeze it down to #1 copper.

Edit: Aluminum is going to be #3/0 to #4/0, 250' & 300'.
 
Last edited:

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
You'll want to check your local code for outlet height depending on the type of building. Many guys here suggest just over 48" so you can lean a piece of 4x whatever material up against the wall and still access the plugs.
 

woodrail

Well-known member
Joined
Feb 23, 2012
Messages
2,456
Location
Lorain, Ohio
Looking for wire size for a 100 amp sub panel. The run will be about 250-300 ft. I have been told several sizes like #4, #3, #1 copper. Or increase the size and run aluminum. Sure would like to no what is the right size to use for voltage drop. Next question is there a standard height for wall outlets. Mainly for the work bench.

OK, I'm going to quit complaining about my 65 foot run. Dude, your going to be in the 4 digit ballpark! :eyecrazy:

I think I would really have to consider the aluminum at this point.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Looking for wire size for a 100 amp sub panel. The run will be about 250-300 ft. I have been told several sizes like #4, #3, #1 copper. Or increase the size and run aluminum. Sure would like to no what is the right size to use for voltage drop. Next question is there a standard height for wall outlets. Mainly for the work bench.

What kind of equipment, HVAC are you going to have out there?
 
OP
M

Monkey Radio

Well-known member
Joined
May 31, 2011
Messages
74
Location
Normandy Park WA
The shop is 26x32. The shop will have three 220 recepticals lift,compreser,welder sixteen wall outlets and six lighting boxes. A couple of outdoor boxes and of course out door lighting. Hopffully that will cover every thing. Did I miss any thing?
 
To avoid these ads, REGISTER NOW!
OP
M

Monkey Radio

Well-known member
Joined
May 31, 2011
Messages
74
Location
Normandy Park WA
General rule is no more than 3% voltage drop. Based on a calculator I have you'd need to use a minimum of #1/0 copper for 300'. 250' you can squeeze it down to #1 copper.

Edit: Aluminum is going to be #3/0 to #4/0, 250' & 300'.[/QUOTE]

The crawlspace run is 80ft. And to the garage is 174ft 254 total. The plane is to run #4 conductor cable to the j-box80ft= 100amps at the box then 2#1HOT 1#2Nutrual and #6GRND. Any thoughts?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The crawlspace run is 80ft. And to the garage is 174ft 254 total. The plane is to run #4 conductor cable to the j-box80ft= 100amps at the box then 2#1HOT 1#2Nutrual and #6GRND. Any thoughts?

I may be misunderstanding your numbers, but 4 gauge copper is only good to 85A.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
Are you sure you want or need 100 amps?

I have a 30 by 50 garage with lift, IR compressor, TIG welder and really think 60 Amps would handle it.

I am a one man operation, so concurrent tool use is limited. Even with plasma I think you would be fine with 60.

I do respect the concept of do it big and do it once however!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I agree with justsam. I think a good compromise would be to use 2/0-2/0-2/0-1 aluminun SER cable for the inside run and the same size Mobile Home Feeder (MHF) for the outside run and into the garage. That will give you up to 80A with less than 3% VD. It will be a lot cheaper than copper.
 
Last edited:

Jamey189

Active member
Joined
Nov 10, 2012
Messages
35
Location
Lake Charles, La
I called my inspector's and told them what I was running 100amp panel 100" away and asked him what i needed to pass his inspection and put what ever he said. He told me to put #1/0 aluminum would be plenty for my application. I'd call the county inspector to ask them.
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Next question is there a standard height for wall outlets. Mainly for the work bench.

No standard heights I know of...I think I recall there being a minimum though. I settled on 24" from the floor to the bottom of the box..IMO nice height. The more outlets I put in, and the more I'm using it, the more I like it.
As for your workbench outlets, it would depend on how high your bench is and its configuration in terms of backsplash etc....
 