wire size

pudgybear

Well-known member
Joined
Aug 22, 2012
Messages
228
Location
Brooklyn Michigan
I am moving a refrigeration cooler compressor at my daughters shop, it will be about 35 foot from the service panel, my question is do i run #12 or #10 wire, the motor draws 56 amps at full load.
 
To avoid these ads, REGISTER NOW!

kd3pc

Well-known member
Joined
Aug 10, 2013
Messages
3,630
Location
Northern Neck
56 amps will require #6 romex or #8 THHN copper (50amps), minimum with appropriate protection and terminations.

Good practice is 125% of what is minimum, which knocks you up a size
 
Last edited:

C96

Well-known member
Joined
Nov 30, 2013
Messages
1,251
Please post a clear picture of the units nameplate.

More info is needed to help you with this.

The NEC has specific rules regarding refrigeration equipment, motors and the like.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Where are you getting the data? Hermetic compressors are frequently marked in locked rotor amperes & sizing to that will result in waaay oversized wiring.
 
To avoid these ads, REGISTER NOW!

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
.... my question is do i run #12 or #10 wire, the motor draws 56 amps at full load.
I know this is an unpopular opinion, but if you have to ask this question you are probably best served calling a pro. ESPECIALLY considering this is a commercial setting.
 