What size wire should I run?
POCO is installing 200amp service to my house
meter/main disconnect;
I will run 150amp into house (1600sqft)to a subpanel
Also from the main disconnect I'm running
100amp to a shop building subPanel(140 ft run) ,
Then from this subpanel running 40amp to a small outbuilding (95 ft run)
The wire will be in buried conduit on both runs.
Also, the 100amp is overkill- 75amp would match
to load calcs; thoughts on which way to go?
The breaker panel at shop building is 125 amp rated