Wire size
Sumboodie
AK
Need to send power to a shed. About 50ft run. Will either come off meter panel or be a subpanel off shop. shop is only 100 amp, #2 wire though, so looking into a 4 breaker meter panel.
It has a 5hp and 3hp air compressor, 2 oil boilers (figure 10 amps each max, more like 5 running), 10 amp air dryer, couple lights, maybe a hanging water to air heater, couple courtesy outlets
My math is working that 60 amp would be more than plenty? #2 4 wire wire is about $3.25 a foot. #4 is about $1 less
wyliesdiesels
Modesto, CA
hopefully the wire is #2 copper. why would you need a 4 space meter main here?
Are you running this all at once?
The 2 compressors alone may be pushing 35-40a. everything else could push you over 60a
#2 cu or al is way overkill for 60a. you would only need #6 THWN or #4 AL w/ #10 cu or #8 al EGC
S
Sumboodie
AK
#2 aluminum is rated to 100 amps for main feeder wire. It's a very common size used here so in stock and not crazy money. 2-2-2-4 SER they call it. 1/0 and 4/0 are fairly common too.
Breaker for future house, current shop, current shed and an outlet at meter required by power company. 4 breakers. May need 5 if I put the generator over by the meter.
Yes, could all be on at once.
#6 THHN x4 wires is around $3.95 a foot plus would need conduit so more money for less capacity. #6 UF is around $6 a foot.
mm08822
#2 AL is only rated for 90a. If you happen to be using the 90C ampacity column then that is wrong to do so b/c the hardware it is connected is only rated for 60/75C.
And for another possible exception that wont apply in your case, feeders are not service entrance conductors.
Norcal
2AWG AL is not rated for 100A, it is allowed under certain criteria to to be used for 100A, none of which the OP meets.
S
Sumboodie
AK
Yes, but it's allow for 100 amp service for the wire from the power company feed to the panel. In my case, from the meter to the house, shop (also a house). But for a shed, 90 amps.
Look up 310.12 in the book.
Granted, that's if I following codes.
I would have run larger wire for the shop, not my doing.
But for the shed, it would be more than plenty and as far as I can find, is cheaper than the minimum #6 copper or #4 aluminum.
mm08822
Yes it does, it's classed as a dwelling.
Doesn't matter what you think anyhow, it's what the local power company wanted and SOP for the area.
Is this set of conductors fed from a cb in the main panel or before the main panel OCP?
mm08822
Or, you're wrong.
Highly doubt 100s of thousands of houses are done wrong.
Based on your description of the interconnections, you don't have service conductors going to your shed. It's a feeder.
I highly doubt you know anything about how 100s of thousands of houses are wired.
NEC 310.12 pertains to single family dwellings, 2 family dwelling units and multi-family units all as part of the same structure. Your separate building (shop) being separate from the single family dwelling makes it a feeder. (Not to mention the cb at the meter main.)
Even if you call it a dwelling, what's in it to make it fit the definition of a dwelling? Kitchen, Full bath, bedroom or just a sleeping bag and teddy bear?
S
Sumboodie
AK
The shop is a dwelling. I currently live in it. There's a 2 bedroom, 1 bath apartment in it.
Never said the shed applied to that. In fact I said just the opposite. Just that I was planning on using #2 feeder wire, mobile home wire, SER, whatever the hell you want to call it, because it's priced well and would be more than enough wire for 60 amps.
S
Sumboodie
AK
And yes I know, my good friend does dirt work and they put in wiring, septic, well piping, foundations, etc. They put in service wires to new places almost everyday 7+ months a year.
75gmck25
Alexandria, VA
AFAIK, 2-2-2-4 AL MHF vs 2-2-2-4 AL SER is really easy to distinguish.
SER cable is jacketed like Romex, so you have a large diameter single cable to route. That makes it simple to route indoors through holes in floor joists, etc. The dual rated MHF that I bought was four separate wires that were spiraled together into a single "assembly", but there was no jacket on the outside. It is usually run in conduit, both indoors (required) and out (not always required).