Ok electricians.....I have a 200 amp panel on my meter pole. I need to run 100 amps to my shop panel that is 160 feet away through 2" conduit. What size wire do I need?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
#3/0-CU for a ~2.5% Voltage drop
#1-CU for a ~4.2% Voltage drop

Not sure if you are getting the 3/0 through 2" or not tho.

Woa nelly! Where'd u get those numbers?

I do the math by hand and got way smaller:

#2 CU will give u a 6.22v or 2.6% drop @ 100a full load.

If the OP wants to use al go with #1/0 al which would give u a 6.43v drop or 2.7%.

So OP u would need 2-2-2-8 CU (the #8 is for the EGC) or 1/0-1/0-1/0-6 AL

OP dont forget 2 rods and a ground bar kit. Also make sure neutral bar is isolated in the subpanel.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Use 2/0-2/0-2/0-1 MHF (Mobile Home Feeder). It's an assembled cable ready to go. Can be direct bury or put in conduit. Best practice is to put in conduit underground, has to be in conduit where above ground. 2" conduit will work.
 

mjbasford

Active member
Joined
Apr 25, 2015
Messages
32
Location
https://t.me/pump_upp
Woa nelly! Where'd u get those numbers?

I do the math by hand and got way smaller:

#2 CU will give u a 6.22v or 2.6% drop @ 100a full load.

If the OP wants to use al go with #1/0 al which would give u a 6.43v drop or 2.7%.

So OP u would need 2-2-2-8 CU (the #8 is for the EGC) or 1/0-1/0-1/0-6 AL

OP dont forget 2 rods and a ground bar kit. Also make sure neutral bar is isolated in the subpanel.

used the southwire online calculator.

http://www.southwire.com/support/voltage-drop-calculator.htm

I did add 10' to his distance tho, to compensate for mis-measuring.

edit: funny, i went back and did again, and i got the same results as you.

Disregard my previous post OP, i am stupid currently.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
The southwire calculator typically uses the 60* c ampacity column. If u do the math yourself u will get better results.
 
OP
T

txturbo

Well-known member
Joined
Jan 14, 2013
Messages
116
Location
Rosenberg,TX
Use 2/0-2/0-2/0-1 MHF (Mobile Home Feeder). It's an assembled cable ready to go. Can be direct bury or put in conduit. Best practice is to put in conduit underground, has to be in conduit where above ground. 2" conduit will work.
i like this option....thanks.....I didn't even think about MHF.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I dont really use those calcs either. My first thought was it got plugged in for 120v.
I have a chart from an electric supply that is super simple, not sure I even know the math to really do it any way, ha, but really do it from memory and simple estimation.
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
I would have real trouble with the math to pass a masters, the other issue is I really don't know anything about electricity. Both a real drawback,, ha
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
I dont really use those calcs either. My first thought was it got plugged in for 120v.
I have a chart from an electric supply that is super simple, not sure I even know the math to really do it any way, ha, but really do it from memory and simple estimation.

The math is easy!

K * 2 * L * C / VD

K=resistance of wire 12.9 for CU 21.2 for AL
L= one way length of wire
C= current or amps
VD= voltage drop. For 240v it would be 7.2, 240 * .03 for 3% = 7.2v

U can replace VD with a specified wire cir mils size to figure out how much voltage drop a given wire size will have. U will need a awg/cir mils chart to do so:

http://www.engineeringtoolbox.com/awg-wire-gauge-circular-mils-d_819.html

So then it would be

K * 2 * L * C / cir mils size
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
It is but I have done this long enough I don't need to do a calc every time I install a wire. I was talking to a guy a while back, claims to do this work all the time and got to look up and calc a ground wire for 200 a servive.
 
OP
T

txturbo

Well-known member
Joined
Jan 14, 2013
Messages
116
Location
Rosenberg,TX
Is there anything in the code that says I can't use un-insulated solid copper ground wire for the EGC going to my sub panel?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Is there anything in the code that says I can't use un-insulated solid copper ground wire for the EGC going to my sub panel?

You can do that. What are you planning to use for the other 3 wires? Nobody around you even carries single conductor aluminum THWN or XHHW or RHH/RHW?
 
OP
T

txturbo

Well-known member
Joined
Jan 14, 2013
Messages
116
Location
Rosenberg,TX
I already have the other wire. I was just asking about the EGC because I have a whole spool of it already.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I already have the other wire. I was just asking about the EGC because I have a whole spool of it already.

What size and type of wire are you using for the "hots" and "neutral"? What size wire is this bare solid copper you're wanting to use?
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
2-2-2 THHN/THWN and the bare copper is #8.

310.106(C) in the 2014 NEC doesn't allow #8 and larger solid wire in conduit unless specifically permitted elsewhere in the code.

It's somewhat of a gray area whether a ground wire meets the requirements.
 