I plan on putting a disconnect on the garage to feed a barn. The barn already has #2 wire running to it , previously had an old farm house where garage is now. Still have that wire buried and will hook to disconnect. I know SE-R can be ran thru the walls without using conduit. Is there anything else that is suitable for this application?
 
To avoid these ads, REGISTER NOW!
OP
T

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
What are you asking?

What type wire is ok to run from breaker box thru stud wall to put a disconnect on outside of garage? I know SE-R cable is approved for that use but what else is?

Hope I made the question clear.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Ah, OK. So you will dig up the old buried #2, put it into conduit (for the part that runs out of the ground) and turn it up the side of the building into a junction box (or disconnect)- you want to know what you can run from the panel into this junction. (note a splice/junction is fine, dont need a disconnect- the panel in the barn will be the disconnect,)

So this new wire will be entirely inside the building then maybe into a box on the exterior wall....

So SE-R or just NM would be fine I think
 
Last edited:
OP
T

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
Since there is a breaker it is the disconnect. But this isn't the right wire for underground.

Never said it would be underground. This would go from 200 amp panel box to a 100 amp disconnect, from there I have underground wire in conduit.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
Never said it would be underground. This would go from 200 amp panel box to a 100 amp disconnect, from there I have underground wire in conduit.

To be fair your original post was very unclear...for all we knew the reference to 'the application' was that there was SER buried out to the barn and you wanted to use that....
 
OP
T

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
To be fair your original post was very unclear...for all we knew the reference to 'the application' was that there was SER buried out to the barn and you wanted to use that....

Sorry if this part was not clear.

I know SE-R can be ran thru the walls without using conduit. Is there anything else that is suitable for this application?
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Various individual conductors in conduit (THHN/THWN, MHF, etc.) would work, or MC in a large size. But the SER will be the cheapest and easiest. 2-2-2-4 SER gives you 90A so you should decide if 90 is OK or if you really need the 100.

What exactly do you have running to the barn? How many conductors of what size? And how far is it to the barn?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
SER is the best option for the run from the panel to the disconnect box without using conduit. The install methods for SER are the same as NM (Romex), so just be sure it's not exposed to possible physical damage.
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Sounds like a typical 90A application. You could probably get away with 60 but you have the wires for 90... except...

... if it's a permit job, they'll want to see four wires to the barn and you probably only have three.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Sounds like a typical 90A application. You could probably get away with 60 but you have the wires for 90... except...

... if it's a permit job, they'll want to see four wires to the barn and you probably only have three.


Whether its permitted or not it should be 4-wires unless done before 2008 code cycle...
 

AntonLargiader

Well-known member
Joined
Nov 20, 2016
Messages
1,372
Location
Charlottesville, VA
Or you could just say, whether it's permitted or not it should be 4-wire.

Today I bought parts to upgrade my shop oven to 4-wire. It's the way of the future and it's better.
 
OP
T

tom-ky

Well-known member
Joined
Mar 11, 2017
Messages
512
Location
Morgantown, Ky
I know it would be more money but even thought about using THHN in ENT conduit. Anyone see and issue with that? Thought it might be a littler easier to work with.
 