Currently, I have a small well house 6ftX6ft on the back of my acreage with a 1 HP well pump.
It's a 1 HP pump and when I look up the specs for it, it says to use a 15A breaker. (It's 240V). The wires are run overhead and a couple of poles need replacing. My wife doesn't like the overhead wires and wants me to put them underground in conduit.
I have the trench done by someone but I would do the rest. I just talked to my well driller and he said the charts say to use #6 wire since it's 350 feet from the main breaker panel to the well house sub-panel. He also says he always puts 20A breakers on 1 HP pumps even though they can work with a 15A.
My question:
He says I only need to run 3 wires for a well house. But, shouldn't I run a 4th wire for a ground? If so, should I use a #8 wire for that one and #6 for the other 3? However, their's only 3 conductors with the present overhead aluminum wires.
And btw, the well house has a light inside, one outside and has one standard 120V electical outlet inside as well.
It's a 1 HP pump and when I look up the specs for it, it says to use a 15A breaker. (It's 240V). The wires are run overhead and a couple of poles need replacing. My wife doesn't like the overhead wires and wants me to put them underground in conduit.
I have the trench done by someone but I would do the rest. I just talked to my well driller and he said the charts say to use #6 wire since it's 350 feet from the main breaker panel to the well house sub-panel. He also says he always puts 20A breakers on 1 HP pumps even though they can work with a 15A.
My question:
He says I only need to run 3 wires for a well house. But, shouldn't I run a 4th wire for a ground? If so, should I use a #8 wire for that one and #6 for the other 3? However, their's only 3 conductors with the present overhead aluminum wires.
And btw, the well house has a light inside, one outside and has one standard 120V electical outlet inside as well.