Wire type for underground?

deepstuff

Well-known member
Joined
Apr 29, 2014
Messages
120
Location
Newfoundland, Canada
What type of wire do I need to pass underground from my house to garage about 20 feet? Should it be ran inside a pipe? Should I use some sort of pipe for slab penetraton?
 
To avoid these ads, REGISTER NOW!

RickP

Well-known member
Joined
Jan 15, 2013
Messages
1,550
Location
Annapolis, MD
MHF is probably your cheapest option. It's direct burial without conduit outside, but it needs conduit inside the house and garage.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Conduit size depends on the wire size used for the amount of power needed. Not knowing the power required and assuming a typical homeowner garage, I'd say stub up 2" PVC at least. Do you know how much power you want in the garage?

Edit: I suggest doing conduit all the way underground and using THHN/THWN wire. I believe the Canadian type for THHN/THWN is T90.
 
Last edited:
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,202
Location
SE MI
I'll b connecting to 6/3 wire already ran to corner of attached garage. Then 30 feet to detached. I figure 60 amps.

If this is copper cable, you need to be careful using MHF because it is aluminum. For 6 gauge I would recommend Polris connectors similar to this

2351d1202137233-polaris-connectors-underground-polaris.png


There are special coatings/grease for aluminum cable when you put it in a connector.

UF-B (direct bury Romex) does come in 6/3 also and then you can use split bolts.
 

nh_yota

Well-known member
Joined
Mar 10, 2015
Messages
4,077
Location
Seacoast New Hampshire
I'm a big fan of using conduit as opposed to direct burial because if you need to re-run the wire for whatever reason you just pull it through with no digging required. PVC conduit is cheap.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Good tips,but the recommended US wire not used in Canada.Your choices are Teck90 or ACWU cable which can be direct buried,or NMWU90 cable or individual RW90 conductors in PCV conduit.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
What type of wire do I need to pass underground from my house to garage about 20 feet? Should it be ran inside a pipe? Should I use some sort of pipe for slab penetraton?

It all depends on what your amperage requirements are.
Some people immediately suggest the "GJ default" MHF route, which would not always be the right choice.
 