Hello, I have a Senville Aura 24k BTU mini split heat pump being delivered for my garage tomorrow that requires a 30 amp 240v breaker and 10/2 wire. I just picked up a 60 amp non fusible disconnect box and I have to run a new line from the breaker to the box.

Can I just run Southwire 10/2 Romex nm-b wire for this, or do I need outdoor rated wire since this will go to the disconnect box outside? I am planning to just run the wire up from the panel into the attic and then drill down at the condenser location and run it down the wall and out right outside directly into the back of the disconnect box.

If I need outdoor wire, what type should I be getting, and do I use the outdoor wire for the entire run from the breaker panel? I just want to make sure I'm using the proper wire that would be required so I don't have any issues in the future.

Thanks!
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
NM-b is fine into the disconnect box. Afterall, think about all the exterior meter mains with NM-b running into them.

From the disconnect box to the condensor, you will need outdoor wire.
 
OP
S

SLAYER6669

Member
Joined
Mar 12, 2013
Messages
20
Location
Toms River, NJ
Yeah I figured as much since it's technically all concealed. I purchased an electrical whip which says thwn thhn wire from the disconnect to the condenser. Appreciate everyone clarifying for me :thumbup:

I have 100' of Southwire 10/2 coming for $75 shipped (with tax) from ebay instead of $121+tax at the box stores. Pretty big difference in price!
 