I'm relocating the 200A main service panel (now a subpanel) 75' to the other end of my home. I've installed a cut-off panel (next to the meter) and would like to connect that panel to the sub with 2" PVC(?) conduit thru the attic. Yes, I'm aware that it's not required when using SER, but I've learned never to underestimate the resourcefulness of bushy-tailed tree rats! So here's my question...I was planning on using AL 4/0,4/0,4/0,2/0 SER wire but now I'm wondering if there's another wire type to consider? I was fine until I started browsing the wire & cable your way website, now I'm :headscrat. Any suggestions so I can move on to obsessing about other things on the remodel? Thanks! :thumbup:
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,925
Location
NW Iowa
Use individual xhhw aluminum conductors. I would pull 4/0, 4/0, 2/0, 4.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Use individual xhhw aluminum conductors. I would pull 4/0, 4/0, 2/0, 4.


Check with your local codes, at least where I am at, we are not allowed to use a derated neutral anymore in residential. But yes, I also agree on the XHHW
 
To avoid these ads, REGISTER NOW!
OP
G

gatorgrabber

Well-known member
Joined
Oct 16, 2011
Messages
285
Location
Gainesville, FL
Thanks for the input, I'll check the codes tomorrow. FWIW, I do know the incoming wires to the meter are 4/0,4/0,2/0. I do like this approach over the SER.
 