I have a question for any pros out there that don't mind answering a question or two for me.
I am currently wiring my new shop. It's a 40' X 64' building (pole barn).
I am running 20A 120V circuits for outlets along the opposite wall (64' away). If I count going up the wall and down the opposite wall, my furthest outlet is about 100ft away.
The wire size calculator that I am using is calling out #8 wire.
#8 wire seems big, especially when terminating to an outlet even in a deep box. It's probably too late for me on this project, but I would still like to know what others have done when running a 20A 120V circuit over a long distance.
The original wire to the outlets the previous owner had was #12. My wire size calculator also calls out #8 if it was only 15A as well, but says that I could go to 153' #8 at 15A.
Another question I have is wire for lighting. I want to put in some 3-way switches for my overhead lighting. How would I measure the distance? From breaker to the light switches then to the lights????
Any opinions?
I am currently wiring my new shop. It's a 40' X 64' building (pole barn).
I am running 20A 120V circuits for outlets along the opposite wall (64' away). If I count going up the wall and down the opposite wall, my furthest outlet is about 100ft away.
The wire size calculator that I am using is calling out #8 wire.
#8 wire seems big, especially when terminating to an outlet even in a deep box. It's probably too late for me on this project, but I would still like to know what others have done when running a 20A 120V circuit over a long distance.
The original wire to the outlets the previous owner had was #12. My wire size calculator also calls out #8 if it was only 15A as well, but says that I could go to 153' #8 at 15A.
Another question I have is wire for lighting. I want to put in some 3-way switches for my overhead lighting. How would I measure the distance? From breaker to the light switches then to the lights????
Any opinions?