Ok just need a quick double check as I’m installing several 6-50r receptacles in my shop.

Wire I’m using is 8/3 with ground. So it has 3 - 8 gauge wires, w r b. And then a 12 ga bare ground.

Most receptacles are fed from sub panels where the ground n neutral are not bonded together (they are fed from my main panel that gr n neutral are bonded together.

In the sub panels I’m connecting hots to breakers white to unbonded neutral and bare ground to ground bar.

Question, at the receptacle I’m wiring the red n black hots to the normal pins but the gr pin is where I’m not sure, do I use the 12ga bare ground or white 8 ga neutral?
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
6-50 doesn't have a neutral. Could have used 8-2. Just cap the white. FYI the bare wire is #10 not #12
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Thanks. I guess I’ll be good if someday I need to convert to a 14-50 receptacle on any of them..

But there is little need for it, people add a unneeded neutral for 240V circuits, 'cause it might be needed but unless it's a range, dryer, Hoshizaki 208-230V single phase ice machine, it is not needed, and if wanting a 15-20A 120 volt convenience outlet, one cannot simply add one to a 30/50A circuit without protection.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
What is the intended use of these 6-50 outlets? You said you are using #8/3 with ground which is NM and is only good to 40A. I assume for welder use only? Also #8 NM should have a #10 ground. #12 for a ground is only good for up to 20A circuits. The white wire is not to be used for a ground, needs to be green or bare.
 
Last edited:

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
Several runs of #8 on a 6-50P would be great for several 8kW portable electric heaters. :)

A welding machine that needs #8, will also need a much larger breaker than a 50A.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
What is the intended use of these 6-50 outlets? You said you are using #8/3 with ground which is NM and is only good to 40A. I assume for welder use only? Also #8 NM should have a #10 ground. #12 for a ground is only good for up to 20A circuits. The white wire is not to be used for a ground, needs to be green or bare.

beat me to it. #8 NM-b limited to 40a...
 