Wiring a compressor
akpolaris
Seward, Ak
I have a new Dewalt compressor that has a 3.5 hp motor and draws 17 amps. It is 220 volts. I believe it needs to be wired into a 2 pole 20 amp breaker. Can I use 12/2 to feed it? The connections show 2 hot wires feeding the motor and there are 2 screws on the plate with ground emblems indicated at each. Do I use 2 hots and a neutral to the plate? This would eliminate the ground from the wiring to the compressor. Then a 20 amp wall plug could function as the disconnect? The owners manual was very vague just directing an electrician do the wiring.
k-os
WI
Another piece of information people will need to know to answer your question is how long of a run it will be from your breaker to your compressor.
A
akpolaris
Seward, Ak
Got it. I figured it would be 30 amp breaker, #10 wire and a disconnect switch. I planned a sub panel where the compressor is going and to run this 1 circuit would be $$ and work that would be torn out when the sub panel goes in later. Guess it is best to temporarily relocate the unit until I am ready for the sub panel
pattenp
Virginia - USA
If the sub-panel is going to be close to the comp you can forgo the disconnect switch. Hardwire the comp using a junction box with a cover plate that has a knockout.
md21722
Mt Juliet, TN
The NEC does not have a FLC amperage rating for motors that have SPL listed in the HP box of on the motor data plate. I suspect 3.5 HP is on a label on the compressor somewhere.
Figuring continuous load, 17A x 125% = 21.25A which is suitable for 12/2 wire per the NEC tables that say 12 gauge is good for 25A.
I do think that most folks just use 10 gauge for this application though...
pattenp
Virginia - USA
You need to be clear in what you say. The designation 12/2 is a NM-b identifier and 12/2 NM-b is good to 20A not 25A. #12 THHN is good to 25A. The reason is NM-b is sized by 60deg C whereas THHN is 75deg C.
When that happens, u look at the FLA on the motor nameplate and then correspond that to the NEC FLC tables to figure out what the HP is closest to. 3HP motor has an FLC of 17a.
Norcal
12/2 wire would be NM cable "Romex®" and the NEC specifies that the ampacity be sized in the 60° column which limits 12 AWG NM cable to 20A. See 334.80
RacerRick
Durham Region, Ontario, Canada
I just did a similar compressor - 3.8hp motor on it, on a pretty long run of about 80 feet from the panel.
I used 10/2 AC90 to a disconnect box, then used the cording that came with the compressor from the box to the compressor. The compressor cord is a very flexible stranded copper and the conductor is about twice the size of the 10-2 conductors. Its on its own 20amp breaker and hasn't tripped it yet.
Norcal
Using flexible cord without a plug does not comply with the NEC, can't comment about the CEC.