My current pump failed and overflowed. I got a new one but this one has two wires for a safety switch where the old one did not. I assume I need to hook these up into the 24 volt thermost circuit for it to work because after being plugged in and filled with water, the pump does not turn on. My stat is a Honeywell RTH2510 and has four wires: red, green, white yellow. Or, is this something I should leave to someone who knows what they are doing?
 
To avoid these ads, REGISTER NOW!

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I'd wire the red wire going out to the condensing unit for ac through those 2 wires.
Make sure to pull out the cardboard for the switch if its sticking out of pump.
 
OP
8

87GN

Well-known member
Joined
Jun 10, 2005
Messages
681
Location
phila, pa
Thanks. Already pulled the cardboard strip out. Red wire, got to the terminal board in the furnace or at the stat. My stat is literally on the wall separating the heater closet from the living room, so about 4 feet from the stat to where the wires inter the furnace.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
The safety switch wires on all the standard type pumps I've run across do not need to be hooked up for it to operate, some of the mini split pumps may have extra wires that need to be hooked up but the regular pumps don't care. Did you fill the pump completely? Most don't come on until they are almost full.

Sent from my SM-G965U using Tapatalk
 
OP
8

87GN

Well-known member
Joined
Jun 10, 2005
Messages
681
Location
phila, pa
I'll be damned, didn't fill it enough. Now it works. The one I took out was hard wired and the green wire, although connected at the switch under the cover, was cut off at the other end of the conduit and not connected to anything. Now, do I really need the safety switch connected since the old unit didn't have one?
 

Attachments

  • DSC04884.jpg
    DSC04884.jpg
    137.2 KB · Views: 57
  • DSC04885.jpg
    DSC04885.jpg
    135.3 KB · Views: 48

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Thanks. Already pulled the cardboard strip out. Red wire, got to the terminal board in the furnace or at the stat. My stat is literally on the wall separating the heater closet from the living room, so about 4 feet from the stat to where the wires inter the furnace.

Do it on the 2 conductor wire to/from the outside unit,not the furnace.
Unless of course you have a 90 plus furnace drain running into the pump.
That way you dont have to worry about causing furnace problems in winter if pump acts up.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
The safety switch will prevent a mess caused by a malfunction of the pump.

Wire it on the yellow (Y) wire in serie between the thermostat and wherever it goes first (condenser or junction board/box or whatever.)

If the pump fails, the A/C will shut off.
 

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
The switch on the pump is to interrupt the 24 signal -- this will turn off the AC should the pump fail. It's to avoid a flood of water -- typically above a ceiling ...etc.

They do not need to be used for the pump to work
 
To avoid these ads, REGISTER NOW!
OP
8

87GN

Well-known member
Joined
Jun 10, 2005
Messages
681
Location
phila, pa
Thanks for all the replies. So i use the red wire??? I'll take a trip to the orange store and buy a couple of feet of t-stat wire.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
The practice used to be to use the yellow wire to the condenser because it allowed the air handler to stay on, but shut off the cooling if the pump stopped. Now that there are condensing furnaces, you use the red wire so it shuts off the cooling or the heat.

Tommy
 
Last edited:

4x4Petr

Member
Joined
Mar 30, 2019
Messages
18
Location
Innisfil ON
Be cautious using the safety switch. It can prevent water damage which is good, but when used on the R wire it will shut off your furnace which could lead to frozen pipes if you were away in the winter. I suggest using the safety switch when water damage is unacceptable and your house is being monitored either by family, friends or an alarm system with a temperature alarm.
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,835
When you switch the red, the thermostat is usually shows dead also and is a good hint at what the problem is. If just the Y wire then things would be working but you could have to troubleshoot a lot more of the system to finally see the pump full.
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
When you switch the red, the thermostat is usually shows dead also and is a good hint at what the problem is. If just the Y wire then things would be working but you could have to troubleshoot a lot more of the system to finally see the pump full.



Well you wouldnt have A/C, people are usually quick to notice. ;)
 
OP
8

87GN

Well-known member
Joined
Jun 10, 2005
Messages
681
Location
phila, pa
Thanks all. Since the old pump did not have a safety switch at all, for the time being, I'll leave the new one the same way.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,311
Location
Beautiful Southern Maryland
The float switch on mine stuck this morning and it overflowed. It happens about every two years or so. We notice it pretty quickly because it is in the hall going to the garage. Doesnt hurt much.

I keep thinking about hooking the safety switch up but I have to weigh the pros and cons. Mainly during the winter if we go away for a week and the furnace stops running what will happen ? I think I would rather have some water on the floor than frozen pipes. So I leave it like it is :)
 

Ohmthis

Well-known member
Joined
Jan 20, 2013
Messages
3,009
Location
Outside of Louisville KY
^^^^^ Bill you can get a WiFi Tstat that can send you alerts. It can save a lot of headaches. Some aren’t too speedy and you can set/play with temps remotely too.
 