Hello everyone I have followed this forum for quite some time. But just made an account and. Today happens to be the day I received my first car lift for my garage. My lift is 3 hp 220volts 60hertz and is recommended a 20 amp breaker. I’ve never used anything with 220volts and I’m no expert at electrical work but I know some knowledge and I’m looking for some assistance with this. I chose 220volts because I heard better results. I plan to run a new outlet from my service panel. My service panel is on the outside of my house and my lift outlet is on the other side. So I don’t think it will be to difficult.
What I think my plan is to run 10 Gauge 4 wire with a 20 amp breaker ( my thinking is thicker wire incase in the future I decide I can upgrade breaker for bigger needs).
I picked up a 4 prong outlet from Home Depot rated 125v/250v. Now my question is the wiring coming out of my lift is 3 wires. When I was doing research I thought the code changed in 1996 to require 4 wires. What do I do to change 3 wires to 4 and add a plug? This is mostly a dry run if anyone has suggestions or recommendations I would greatly appreciate it.

Here is my outlet:

Here are wires coming out of my lift control panel:
 

Attachments

  • 16101F13-4D5C-4014-AF35-3B0370189578.jpg
    16101F13-4D5C-4014-AF35-3B0370189578.jpg
    67.7 KB · Views: 14
  • 72D20E15-492A-4F05-A8BD-C1AEAEB6DB8D.jpg
    72D20E15-492A-4F05-A8BD-C1AEAEB6DB8D.jpg
    61.1 KB · Views: 26
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,256
Location
Modesto, CA
You dont need a 4-wire outlet for a 240v lift. A 240v motor does not have nor needs a neutral.

The 3-wire to 4-wire 96’ code change you're referring to is in regards to ranges and dryers. Doesnt apply here....

Get a 6-30r and p.
 
OP
S

Seanofdead

New member
Joined
Feb 2, 2021
Messages
2
Location
Las Vegas
You dont need a 4-wire outlet for a 240v lift. A 240v motor does not have nor needs a neutral.

The 3-wire to 4-wire 96’ code change you're referring to is in regards to ranges and dryers. Doesnt apply here....

Get a 6-30r and p.

Ok awesome! Thank you now does that make a difference on wiring I run from the new breaker? My 10/4 and I ended up going with has 4 wires I know I connect the red and black to the new 6-30r and then the ground. What about the neutral white wire?
 