I'm planning on wiring my workshop to the main panel in my home. They are separated by 275 feet (so 550 feet total circuit distance). I'd like a 100A feeder.
Calculations from http://www.csgnetwork.com/wiresizecalc.html indicate I'll need at least 350 mcm for AL. I've seen guidance on this site recommending a smaller DIA wire for similar installations. Why the discrepancy? Am I missing something? 350 mcm would push me to XHHW while I'd like to use Mobile Home Feeder if I could get by with 4/0.
If I go with 350 mcm XHHW I'd like to purchase one long spool of black wire and use this wire for the 3-conductors (maybe ground too). Can this be done according to code as long as the ends exiting the conduit are color coded appropriately?
Calculations from http://www.csgnetwork.com/wiresizecalc.html indicate I'll need at least 350 mcm for AL. I've seen guidance on this site recommending a smaller DIA wire for similar installations. Why the discrepancy? Am I missing something? 350 mcm would push me to XHHW while I'd like to use Mobile Home Feeder if I could get by with 4/0.