Picked up a new compressor for the shop, 7.5hp single phase. I need help picking out what wire to order. It says #6 wire if under 50 ft or #4 if over 50 ft. I will be right at 60 ft from the breaker box. I have a 200 amp service and want to use wire that is in the flexible metal coving to avoid conduit. Suggestion on where to buy and which size? Example- would i need 6/4 or 6/3 etc.

Thanks for your help
 

Attachments

  • IMG_3840.png
    IMG_3840.png
    4.5 MB · Views: 32
To avoid these ads, REGISTER NOW!
OP
S

speedshop

Member
Joined
Nov 11, 2023
Messages
11
I will be running the cable on a steel beam 10’ up so not concerned about not being in conduit.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
Here is the product page


32 amp running
50 amp breaker
motor circuits are sized by HP NOT running amps or nameplate amps

wire is sized by 125% of HP FLC table amps

for 7.5HP thats 40 x 1.25 = 50a rated wire. #8 THWN in conduit or 6/2 NM-b

breaker can be max 250% of FLC amps so 100a

will need to be hardwired. nema plug not rated for 7.5hp

will also need a disconnect if not within sight of and further than 50' from breaker panel
 
OP
S

speedshop

Member
Joined
Nov 11, 2023
Messages
11
how do you plan to secure the NM-b then
motor circuits are sized by HP NOT running amps or nameplate amps

wire is sized by 125% of HP FLC table amps

for 7.5HP thats 40 x 1.25 = 50a rated wire. #8 THWN in conduit or 6/2 NM-b

breaker can be max 250% of FLC amps so 100a

will need to be hardwired. nema plug not rated for 7.5hp

will also need a disconnect if not within sight of and further than 50' from breaker panel
Thanks
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,941
Location
NJ
EMT would work and look much better. You already have some on the wall.
 