Hi, I’m looking for a check on my figuring.
2 or 3 questions (2 are related to each other)
I have a Lincoln 180 that I need an outlet for. It will be located where about 30 feet of wire will be needed to connect it from the CB panel to the outlet. The manual for the mig says that the standard voltage is 230v (I have about 220 measured, if it matters), input current at rated output (which is 130 amps output), is 20 amps. I’m not sure how many amps will be drawn at the advertised maximum of 180 amps out. The manual recommends a 40 amp Super Lag breaker.
I figure I need 8ga NM on the 40 amp breaker. Is this correct? Overkill?
And on the mig, if I should want to use it more than 6 or so feet away from the outlet, I would need an extension cord. A few calculators I’ve used suggest 10ga cord for up to 100 feet at rated amperage. Is this correct? Underkill?
Also, I have a compressor that I need to wire. It’s a 5HP IR, FLA 21.5, 230 volt 1 ph located about 40 feet of wiring away. NEC 430.248 says 5HP at 230V FLA is 28, but the dataplate on the motor says 21.5. I used 430.248/28 FLA. Per 430.22, multiplied 28 with 1.25 and came up with 35 amps, the minimum wiring size as 8ga NM. Breaker size 40. Is this correct? Overkill? A few other people I know ran wiring of 10ga and 30 amp breaker, but it looks to me that I need 8 and 40.
Thanks in advance.
Bill
2 or 3 questions (2 are related to each other)
I have a Lincoln 180 that I need an outlet for. It will be located where about 30 feet of wire will be needed to connect it from the CB panel to the outlet. The manual for the mig says that the standard voltage is 230v (I have about 220 measured, if it matters), input current at rated output (which is 130 amps output), is 20 amps. I’m not sure how many amps will be drawn at the advertised maximum of 180 amps out. The manual recommends a 40 amp Super Lag breaker.
I figure I need 8ga NM on the 40 amp breaker. Is this correct? Overkill?
And on the mig, if I should want to use it more than 6 or so feet away from the outlet, I would need an extension cord. A few calculators I’ve used suggest 10ga cord for up to 100 feet at rated amperage. Is this correct? Underkill?
Also, I have a compressor that I need to wire. It’s a 5HP IR, FLA 21.5, 230 volt 1 ph located about 40 feet of wiring away. NEC 430.248 says 5HP at 230V FLA is 28, but the dataplate on the motor says 21.5. I used 430.248/28 FLA. Per 430.22, multiplied 28 with 1.25 and came up with 35 amps, the minimum wiring size as 8ga NM. Breaker size 40. Is this correct? Overkill? A few other people I know ran wiring of 10ga and 30 amp breaker, but it looks to me that I need 8 and 40.
Thanks in advance.
Bill