Im installing another circuit in garage.
For a 240vac 26a pottery kiln.
When on it will run at full load (26a) for up to 10 hours at a time.
I asked what safety factor they used. They said none, that it pulls a full 26a.
They recommend a 30a breaker.
I have a spare 30 dbl for my panel,so that would be good,but is 30 really enough?
I will need x' of wire.
Mounting wire on (not in) garage inside wall.
What type & gauge wire?
Does code requires Conduit and if so why?
Id need to install a Kwh meter for the kiln. I see so many for sale 8 to 25$. I'm not sure if any are decent quality. I also see house meters used tested guaranteed for 25 to 40$. But then Id need a box too and think maybe I'm going over kill doing that.

Your thoughts?

Tks,
Paul
 
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Constant loads should have circuits sized for 80% derating, so 26/0.80=32.5
If they say 30a breaker, I'd do that, but I would up size from #10.

Conduit is needed if the wire is subject to damage or if you are in a jurisdiction that requires it, like Chicago

Why do you need a meter? Something like an Emporia vue would let you track usage and can handle that load no problem
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,422
Location
Beautiful Southern Maryland
Are you sure it actually runs at 26 amps continuosly ? I would think it would get up to temperature and then cycle on and off to keep at temp. One of my friends Wife has a ceramic kiln and knowing him it is plugged into his welder outlet when needed :)
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
Oops i meant to post the footage. Measures 25, so lets say 3o to be safe.

It does cycle some,but mostly on.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
It's discontinued,but manufacturer says 26. There is no plate on it. :(
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
If it trips the breaker and i have to get a 35 or 40, then what gauge and type wire I need?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
25' coils are commonly available. I'd try to measure it out with a string and see if you can make it work

8/2 nm-b for a 40. I'd do 8/2 and a 30, to align with their spec
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
8/2 on a 30A breaker sounds good. But you want to know how to install this. It will need to be in a conduit if on the surface. Will you hard wire the kiln or does it have a plug? This is a whole 'nother discussion.

If wire in conduit you will use stranded.
 
Last edited:
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
It has 6awg cord and 50amp 3 prong plug. Manufacturer says they must have been replaced. Im concerned that this might pull more then 26.

To track power used.

Why stranded wire in conduit.

From what i read even if it only pulls 26, that breaker could over heat if not x 1.25
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
I just measured kiln resistance on highest setting. 9.3 ohms makes for 25.8 amps. 26 x 1.25 is 32.5. so a 35 amp breaker. So 25' of 8awg. Thwn, use or any 8 awg?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Cost wise I'd use 6-6 w/g Aluminum SER. I believe #6 is the smallest two wire SER you can get. If the cable is installed in an area that it may be subject to possible damage just sleeve it in conduit or run it along the side of a running board.
 
OP
P

paulmars

Well-known member
Joined
Jun 7, 2013
Messages
207
Could i use "8 AWG Copper 2 Conducter Black & White w/10 AWG Ground Wire"?

Is alum cheaper?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Could i use "8 AWG Copper 2 Conducter Black & White w/10 AWG Ground Wire"?

Is alum cheaper?
Aluminum is cheaper, but requires going up at least one wire gauge. So #8 copper or #6 aluminum.

Copper
https://www.wireandcableyourway.com/8-2-w-g-nm-b-wire-black

Aluminum
 