Hey guyz. Great site. First post so here goes. Wiring my new garage
i am wanting to run two always on plug ins and three switched lights off the same circuit and all coming out of the same junction box. Id like to run my power supply into this box for ease of running it. Take a look at what ive drawn up n lemme know what ya think. I am planning on doing this on each side of the garage so i have two banks of lights. Thanks
 

Attachments

  • image.jpg
    image.jpg
    143.4 KB · Views: 100
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Two things I see wrong with your diagram. First, you don't wire lights and outlets in a series. Second, the switch needs to disconnect the lights on the hot side not the neutral side.
 
Last edited:

CADPoint

Well-known member
Joined
Jan 31, 2011
Messages
155
Location
WSW of **** City
Why don't you just run some sizable power out there to a panel. The electrical code allows for another circuit to be run out to garage to control lights. Run 12/3 thhn switch what you want.
 
To avoid these ads, REGISTER NOW!
OP
D

Diggler1979

Member
Joined
Oct 24, 2012
Messages
8
I have a 100 amp panel already in the garage. Just trying to figure out the best
way to run everything. Utilizing my circuits by mixing plug ins and lights.
 

MN Falcon

Well-known member
Joined
Jan 31, 2010
Messages
252
Location
Minneapolis MN
Run outlet circuits separate from light circuits. I have 100amps in my garage also. I have four 20amp outlet circuits with maybe 6 outlets on each. I have two 15amp light circuits. While having 2 light circuits might be overkill, I figured that I could load up on lights and have several switches to control total light usage. Having four 20amp circuits allows use of several high amperage devices with motors, ie my son and I could be running saws at the same time.

At the time I did this and had the electrical inspection I also put in a 20amp dedicated circuit for the heater, a 50amp 220V for the arc welder (reduced protection to 30amp recently for my Hobart 140 mig) and a 20amp 220V circuit for an air compressor.

IIRC code says lights should be protected by 15amp, I don't want to run saws on 15amps while that same circuit has multiple lights on as well.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I have a 100 amp panel already in the garage. Just trying to figure out the best
way to run everything. Utilizing my circuits by mixing plug ins and lights.
While you can mix receptacles and light fixtures in the garage, why do it? I guess you want to simplify feeding the box. The point about having lights on the plug circuit is valid.

You don't want to blow the lights when you have a board in the table saw.
Just my .02
 

Midnight_America

Well-known member
Joined
Oct 19, 2012
Messages
228
Location
Northern Illinois
While the code doesn't prohibit wiring lighting and receptacles on the same circuit for your particular garage project, I would try to avoid it if at all possible. I say keep predictable lighting loads on separate circuits from unpredicatble receptacle loads. You don't want to be working at night in your garage, pop a breaker, and be left in the dark (FYI: Code prohibits lighting on the following receptacle circuits: laundry rooms, kitchen 20A circuits, and 20A bathroom receptacles (bathroom restriction only applies if the bathroom receptacle(s) circuit supplies power to more than 1 bathroom).
 