Question for the electrical aspects of the DIY kits.
Does the 36K units require an 8 AWG wire to be ran or a 10 AWG? From what I’ve read previously everyone said 8, however, my electrician says otherwise. Read on..
I had an electrician come out today to provide an estimate for wiring. He looked at my 36K MrCool DIY unit and said that in North Carolina they do not base the wiring off of the maximum amps. They base the wiring off of the minimum circuit capacity.
The sticker on my 36K unit has 25A minimum capacity and they want to run a 10 AWG wire.
There are two versions of the manual. I’ve attached the screenshots of both. One is from online and the other is came with the unit.
So, do I need to run 10 AWG or 8 for this unit? If 8, why would a trusted electrician say otherwise? I was told I would need to have/show the 8 AWG requirement in writing to justify why it needs to be run (I can use the online version of the manual to prove that if I need to, but it would be more expensive especially because I already have an unused 10 AWG wire in that area they can use).



Does the 36K units require an 8 AWG wire to be ran or a 10 AWG? From what I’ve read previously everyone said 8, however, my electrician says otherwise. Read on..
I had an electrician come out today to provide an estimate for wiring. He looked at my 36K MrCool DIY unit and said that in North Carolina they do not base the wiring off of the maximum amps. They base the wiring off of the minimum circuit capacity.
The sticker on my 36K unit has 25A minimum capacity and they want to run a 10 AWG wire.
There are two versions of the manual. I’ve attached the screenshots of both. One is from online and the other is came with the unit.
So, do I need to run 10 AWG or 8 for this unit? If 8, why would a trusted electrician say otherwise? I was told I would need to have/show the 8 AWG requirement in writing to justify why it needs to be run (I can use the online version of the manual to prove that if I need to, but it would be more expensive especially because I already have an unused 10 AWG wire in that area they can use).