Wiring for a welder

2cool2hear

Well-known member
Joined
Aug 19, 2012
Messages
91
I just bought 304 XMT (230/460v) with feeder and now I need to install a dedicated wiring system for the machine, in garage. Can someone tell/show me what wiring system should look like? Or share a good wiring instruction on here?

The plan is to wire it myself and then have a certified electrician inspect it to make sure everything's safe. I'm taking my time to make sure I understand what I'm working with.

For phase 1 and phase 3, from what I understand, typical home use 1 phase, so I'm going with that.

Here's what I get from the manual:

60 Hz Single Phase #1
Input Voltage: 230
Input Amperes At Rated Output: 53
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 60
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 80
Min Input Conductor Size in AWK/Kcmil: 8
Max Recommended Input Conductor Length In Feet (Meters): 85 (26)
Min Grounding Conductor Size in AWG/Kcmil: 8

60 Hz Single Phase #2
Input Voltage: 460
Input Amperes At Rated Output: 27
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 30
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 40
Min Input Conductor Size in AWK/Kcmil: 10
Max Recommended Input Conductor Length In Feet (Meters): 224 (68)
Min Grounding Conductor Size in AWG/Kcmil: 10

UPDATED MATERIALS
Time-Delay RK5 fuses rated for 30 or 60amp?
A roll of 8/2 or 10/2 wire?
6-50R receptacle
Line disconnect device/box
Metal junction box for the receptacle
Metal conduit (flexible or rod?)

Other suggestions are welcome.

Thanks
 
Last edited:
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Have you looked up he owners manual at Miller? I don't remember them all but think a 6 circuit @ A is good. If this is close to a panel and since you have a plug I might skip the switch. If it was out of the way in another room and hard wired would add a disconnect but there is no point of adding extra pieces and connections if you don't need them.
 
Last edited:
OP
2

2cool2hear

Well-known member
Joined
Aug 19, 2012
Messages
91
Have you looked up he owners manual at Miller? I don't remember them all but think a 6 circuit @ A is good. If this is close to a panel and since you have a plug I might skip the switch. If it was out of the way in another room and hard wired would add a disconnect but there is no point of adding extra pieces and connections if you don't need them.


For phase 1 and phase 3, from what I understand, typical home use 1 phase, so I'm going with that.

Here's what I get from the manual:

60 Hz Single Phase #1
Input Voltage: 230
Input Amperes At Rated Output: 53
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 60
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 80
Min Input Conductor Size in AWK/Kcmil: 8
Max Recommended Input Conductor Length In Feet (Meters): 85 (26)
Min Grounding Conductor Size in AWG/Kcmil: 8

60 Hz Single Phase #2
Input Voltage: 460
Input Amperes At Rated Output: 27
Max Recommendation Standard Fuse Rating in Amperes Time-Delay: 30
Max Recommendation Standard Fuse Rating in Amperes Normal Operating: 40
Min Input Conductor Size in AWK/Kcmil: 10
Max Recommended Input Conductor Length In Feet (Meters): 224 (68)
Min Grounding Conductor Size in AWG/Kcmil: 10

UPDATED MATERIALS
Time-Delay RK5 fuses rated for 30 or 60amp?
A roll of 8/2 or 10/2 wire?
6-50R receptacle
Line disconnect device/box
Metal junction box for the receptacle
Metal conduit (flexible or rod?)
 
Last edited:
To avoid these ads, REGISTER NOW!

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,794
Location
Connecticut
I just bought 304 XMT (230/460v) with feeder and now I need to install a dedicated wiring system for the machine, in garage. Can someone tell/show me what wiring system should look like? Or share a good wiring instruction on here?

The plan is to wire it myself and then have a certified electrician inspect it to make sure everything's safe. I'm taking my time to make sure I understand what I'm working with.

MATERIALS
50 (or 60?) amp breaker
a roll of 6/2 wire
6-50R receptacle
Metal junction box with disconnect switch (is that called power cutoff box?)
Metal junction box for the receptacle
Metal conduit (flexible or rod?)

Other suggestions are welcome.

Thanks

Read the code on Welders. I have a 6-50R according to code I can wire it with #8 wire and use a 125 Amp breaker based on the duty cycle of my Lincoln Square wave 175. My inspector wanted to reject my welder wiring until I showed him the code.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,764
How do I find out what the input voltage is?

You most likely do not have 480 volts in your garage, set the machine for the 230V taps to use commonly available 240 volt power.
 