juddspaintballs
Well-known member
I'm setting up a 40' 5th wheel RV to live in for a bit while I build a house. It has two AC units and the typical power draw for a giant RV like that. With both AC's running, the whole thing will run on a single 50A plug by drawing two 120v circuits off of that big 4 prong 240v plug.
I bought a Siemens TL137US Temporary Power panel that has a 240v 4-prong 50A socket pre-wired, a 240v 3-prong 30A socket pre-wired, and a 120v GFI 20A outlet. 100A total in this box of pre-wired outlets. I will be using the 50A socket for the RV and probably also the full extent of the 20A plug for other things at the RV. I will probably not be using the 30A socket at all (and yes I realize I can't use it at all on the RV because it is 240v, not 120v like an RV 30A plug needs).
I wanted 2-2-2-4 MHF wire to power this. I have about 120' run from the house's empty sub panel with a 100A breaker in it already. I have a dual 50A breaker to put in to connect the MHF feed to. When I called Rexel to have them cut me 150' of it so I could just swing in and pick it up, the woman cut 2-2-4-6 for me and that's what I wound up paying for as well. I was in a hurry and took it with me anyways. I can probably still source and retrieve 2-2-2-4 somewhere if I need to, but I need to get this wire in the ground ASAP.
Will the 2-2-4-6 be adequate? I can't really "balance" my 120v loads from the RV on the temporary power panel. I assume the RV manufacturer was at least smart enough to put the AC units on separate sides of the plug so they sort of balance out. Without the AC units running, the whole RV takes maybe 20A to power. With the AC units running, I'll assume it requires nearly the full 50A it is specified for. And again, I'll probably find other things to plug into the 20A GFI on the panel, so I'm looking at an overall load of about 70A.
I bought a Siemens TL137US Temporary Power panel that has a 240v 4-prong 50A socket pre-wired, a 240v 3-prong 30A socket pre-wired, and a 120v GFI 20A outlet. 100A total in this box of pre-wired outlets. I will be using the 50A socket for the RV and probably also the full extent of the 20A plug for other things at the RV. I will probably not be using the 30A socket at all (and yes I realize I can't use it at all on the RV because it is 240v, not 120v like an RV 30A plug needs).
I wanted 2-2-2-4 MHF wire to power this. I have about 120' run from the house's empty sub panel with a 100A breaker in it already. I have a dual 50A breaker to put in to connect the MHF feed to. When I called Rexel to have them cut me 150' of it so I could just swing in and pick it up, the woman cut 2-2-4-6 for me and that's what I wound up paying for as well. I was in a hurry and took it with me anyways. I can probably still source and retrieve 2-2-2-4 somewhere if I need to, but I need to get this wire in the ground ASAP.
Will the 2-2-4-6 be adequate? I can't really "balance" my 120v loads from the RV on the temporary power panel. I assume the RV manufacturer was at least smart enough to put the AC units on separate sides of the plug so they sort of balance out. Without the AC units running, the whole RV takes maybe 20A to power. With the AC units running, I'll assume it requires nearly the full 50A it is specified for. And again, I'll probably find other things to plug into the 20A GFI on the panel, so I'm looking at an overall load of about 70A.



), his #2 aluminum cable has an ampacity rating of 75 amps (based on the standard NEC panelboard 60C temp limit for #2 wire).