Wiring for future air compressor

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
See this is what happens when I try to read in a hurry. I read it wrong (and wired it wrong in my install). Re reading it now I see that you all are correct and I would need an appropriately rated protective device between the higher rated circuit and lower rated outlet. I will be adding a 15A fuse in a 30A rated fuse holder to the line that feeds the outlet. Thanks for pointing out my mistake. To anyone reading this later nothing I have said earlier in this thread is correct.


Sent from my iPhone using Tapatalk

To throw in another wrench into the works, if a receptacle is used, GFCI protection is required, since there are no exceptions to GFCI requirements when a receptacle is used.
 
To avoid these ads, REGISTER NOW!

Pwrgeek

Well-known member
Joined
Oct 18, 2015
Messages
288
Location
Texas USA
To throw in another wrench into the works, if a receptacle is used, GFCI protection is required, since there are no exceptions to GFCI requirements when a receptacle is used.


That one I got right. It's a GFCI receptacle


Sent from my iPhone using Tapatalk
 