Quick question - am wiring a feed for a heat pump in 3/4" conduit with THHN wire. FLA of the load is 29.6 amps. I see that the maximum ampacity for #10 THHN is 40A, which would work fine since I happen to have a roll of it already.
Problem is I see several notes about maximum amperage of #10 wire is 30 amps, but I'm not sure if it is referring to the load or to the breaker size. If it's the load I'm within that number, otherwise I'm not.
https://www.lapptannehill.com/resources/technical-information/ampacity-chart
So, the load is 29.6 amps and it needs a 40A breaker to allow for motor starting. Do I need a #8 wire or a #10?
Problem is I see several notes about maximum amperage of #10 wire is 30 amps, but I'm not sure if it is referring to the load or to the breaker size. If it's the load I'm within that number, otherwise I'm not.
https://www.lapptannehill.com/resources/technical-information/ampacity-chart
So, the load is 29.6 amps and it needs a 40A breaker to allow for motor starting. Do I need a #8 wire or a #10?