Would figure the manual would be in metric... I suspect they spec a 25 amp CB or slow-blow fuse to make sure it doesn't nuisance trip on compressor start-up.
In that case I would use 10/2 for the feeder to the outside unit, 30 amp CB in the panel, and a no-fuse disconnect outside next to the unit (I believe that is required within sight of the unit). The "connecting cable" as they call it between the outside and inside units is a tough one. I hesitate to use normal 14/2 romex for that, since it calls for it to be bundled with the refrigerant lines, but I don't think your allowed to use SOOW cord in that type of application either (in wall, permentant installation).
10/2 would be sufficent for any future A/C outside unit, that is very standard (romex to the disconnect, THNN in waterproof conduit between disconnect and unit). I'll have to defer to someone smarter for the connecting cable to the inside unit.