Wiring For Relocated Garage Outlet

bagsanthony

Well-known member
Joined
Sep 2, 2010
Messages
392
I'm in the process of remodeling my garage and its wiring. Prior to this I had a metal outlet (one that you would see for conduit) and it laid right on the wood stud. I'm insulating and putting OSB up in the garage so I had to buy blue wire gang box so that my OSB could sit flush with the outlet cover. When I re-rout the wires now into the top of the gang box, there is about 1-1/2" of exposed wiring , no insulation present feeding into the outlet box just before it enters in. This is because of the relocated outlet cover. Is this 1-1/2" of exposed wiring a problem?
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The outer jacket of the Non Metallic cable needs to continue to inside the box, by a quarter inch or so at least. It the jacket is too short, you need to pull, reroute, replace, do whatever you need to, to get the jacket of the NM to reach the clamp in the box.

Charles
 
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
Can you move the box further up so you do have enough insulation?

Can you mount another receptacle up higher so your wire will reach, and it could then feed your existing one down lower? Any junction box used to splice wires, must be accessible, even if just a cover plate.
 