Wiring for RV 30A & 20A duplex

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
I'm wiring a 30A RV elect panel, rain proof that also has a 20A duplex. Is it code to use the same gnd wire for both the 30A and the 20A?
Using 10 awg for the 30a and 12 awg for the 20a. Wire it in 1/2 EMT.
thanks,
Steve
 

Attachments

  • RV panel.jpg
    RV panel.jpg
    91.8 KB · Views: 64
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,627
Location
Austin, TX
That box has a bus right? I'm confused when you said you're running two feeds to it. I'd expect a single feed, run to the bus, breakers etc.
 
To avoid these ads, REGISTER NOW!
OP
S

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
That box has a bus right? I'm confused when you said you're running two feeds to it. I'd expect a single feed, run to the bus, breakers etc.

Yes is has busbars. The 30a and the 20a are separate. The 20a has provisions for an additional breaker.
 

Attachments

  • inside IMG_2323.jpg
    inside IMG_2323.jpg
    71.3 KB · Views: 50
  • outside IMG_2329.jpg
    outside IMG_2329.jpg
    65.3 KB · Views: 34

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Yes is has busbars. The 30a and the 20a are separate. The 20a has provisions for an additional breaker.

No need to run 2 sepeate circuits then.

Run 2- #8’s and a #10 for the grnd. The neutral will need to be white jacketed and ground will need to be green jacketed. Put it on a 50a breaker. If the EMT is complete all the way to the panel, then you dont even need a grnd wire.
 
OP
S

scout4bta

Well-known member
Joined
Nov 2, 2017
Messages
90
Location
Willcox Arizona
No need to run 2 sepeate circuits then.

Run 2- #8’s and a #10 for the grnd. The neutral will need to be white jacketed and ground will need to be green jacketed. Put it on a 50a breaker. If the EMT is complete all the way to the panel, then you dont even need a grnd wire.
Yes every thing is in EMT, metal workshop.
Got it.
Thanks.
 