Wiring for sub panel

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.

wow nice neighbor! that stuffs not cheap. first thing, is what is the wire type. Is it THHN/THWN? You need 4 lines to the sub panel, 2 hots, a neutral, and a ground. You need to check the charts and do any derating for distance, but you should be good for 90-100amps. Use the #2 for hots, and neutral. Then get some #6 for the ground (check to make sure #6 is the right size) Your 2" conduit is plenty large.
 

redsky49

Well-known member
Joined
Jan 21, 2009
Messages
582
Location
near the coast in eastern North Carolina
Just curious

If the normal current carrying wires (neutral and hot) are properly sized at #2, why is it that the ground conductor should be a smaller size?

In the event of a ground fault, say at an appliance with a poor ground, this conductor should theoretically carry the fault current safely to ground. In the case of a serious short circuit, this grounding conductor could have the full circuit current flowing it. Doesn't this present a danger to occupants, and isn't this even more important when dealing with higher amperage (240V, 208-460V) circuits?

What are your thoughts mrb?:headscrat
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
No,code only requires #8 ground for up to 100A,however it must be mechanically protected so most just use #6 to save time and material. Theoretically the ground conductor will only see the fault current instaneously,that is one of the reasons it is considerably smaller.
Voltage has no bearing on the size of a conductor, amperage, length and the conditions the conductor is placed in determine the size.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Code allows a undersized ground, as it will not be carrying the current for long.

Be sure and identify the neutral with white/grey tape around the ends.

Charles
 
Last edited:

GSSFC

Well-known member
Joined
Apr 13, 2008
Messages
423
Location
Wolfeboro, NH
After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.

These are insulated or bare copper? Probably a dumb question!

Tim
 
OP
B

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
Insulated copper wire.

mrb...THHN, He was told to get rid of it, so he asked if I could use it, then tossed it over the fence for me.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
Bevis, make sure that wire is dual rated as THWN also. If it's straight rated THHN(which I've never seen) you can't use it in a wet location(i.e. underground in conduit).

If the insulation checks out, I'd try to get 2 runs out of one of the rolls and use the #2 for a ground wire also. It'll save you from buying anymore wire.
You'll need a collar strap most likely to fit the #2 wire on your ground bar. Siemens part #ECCS1. I only remember that because I bought one this morning....:)
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
Bevis, make sure that wire is dual rated as THWN also. If it's straight rated THHN(which I've never seen) you can't use it in a wet location(i.e. underground in conduit).

If the insulation checks out, I'd try to get 2 runs out of one of the rolls and use the #2 for a ground wire also. It'll save you from buying anymore wire.
You'll need a collar strap most likely to fit the #2 wire on your ground bar. Siemens part #ECCS1. I only remember that because I bought one this morning....:)

I would save the longest piece of #2, buy the #8 needed for the ground, and sell the #2
 

PGBioD

Member
Joined
Jan 24, 2009
Messages
8
Location
The Land Between Two Rivers, USA
You don't need to run the safety ground all the way back to the 'main'.
But you do need to drive a ground rod right near the sub-panel and attach your wire.
Just get the regular bare ground wire.
Much easier, safer, and cheaper.

Goodluck
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
You don't need to run the safety ground all the way back to the 'main'.
But you do need to drive a ground rod right near the sub-panel and attach your wire.
Just get the regular bare ground wire.
Much easier, safer, and cheaper.

Goodluck

you do need to run the ground back to the main, as well as drive a ground rod at the detached structure.

make sure you keep your neutral and ground seperate at the sub panel
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
You don't need to run the safety ground all the way back to the 'main'.

You may want to double check on that piece of advice.Feel free to give us examples where that would be permissable by code.
 
Last edited:
To avoid these ads, REGISTER NOW!

Torque1st

MEMBER EMERITUS
Joined
Sep 14, 2008
Messages
5,668
Location
KC Metro, Kansas
You may want to double check on that piece of advice.Feel free to give us examples where that would be permissable by code.
EDIT- OOPS I read it wrong. A ground wire IS required with a single 110 circuit but a ground rod is not required. That is by the ancient pre-millenium code.

The site below is excellent but they must be making some site changes. The 2002 code article is not available anymore so the following is the newest they have at the moment.

http://www.selfhelpandmore.com/1999...o-dwellings/wiring-a-detached-garage-1999.php

With 220 a ground wire and a ground rod is required.
 
Last edited:

mad57

Well-known member
Joined
Jan 30, 2009
Messages
1,698
Its Now Code In Nj To Put 2 Grounding Rods 6 Ft Apart,fyi. Also Why Not Put It Through Conduit? Its Cheap And Protects The Buried Wire, Just Make Sure To Tape Your Grounds With White Tape On Both Ends Before Pulling Through The Pipe, Good Luck,mike.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Its Now Code In Nj To Put 2 Grounding Rods 6 Ft Apart,fyi. Also Why Not Put It Through Conduit? Its Cheap And Protects The Buried Wire, Just Make Sure To Tape Your Grounds With White Tape On Both Ends Before Pulling Through The Pipe, Good Luck,mike.

Neutral gets the white or grey tape markings on the end (if the wire is not already properly color coded), not the ground, which must be green, green/yellow striped, etc as specified in the code.

Charles
 
OP
B

Bevis

Well-known member
Joined
Jan 10, 2006
Messages
808
Location
Moore Haven, Florida
Got the conduit in the ground this morning before the rain started...Pulled out wire to pull thru conduit and found that the #2 cable had been cut right in the middle of two runs. Can this THNN/THWN copper be spliced undergound?? If not guess I;ll be buying 120' run of #2 (60' x 2).
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Code calls for 1 rod if you can meet 23 ohms or less resistance, if not you use 2. Its simple and easier to just use 2 and as Torque eluded to some places just require 2 due to the local soil conditions. There are even places where 3 wire panels fed from existing service may be acceptable but for this crowd they should be 4 wire period. There are just too many possibilities to mess up the grounding system and provide for alternate current pathways that a 4 wire system just plain eliminates a lot of confusion.
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,674
Location
Maine
Code calls for 1 rod if you can meet 23 ohms or less resistance, if not you use 2. Its simple and easier to just use 2 and as Torque eluded to some places just require 2 due to the local soil conditions. .

Thats for a service, does it hold true for a sub panel?
 

nate379

Banned
Joined
Feb 2, 2009
Messages
7,279
Location
Palmer, AK
I didn't know that a sub panel needed it's own rod though.

What's the reason for that?? Running a ground from the subpanel to the main would tie it to the main panel's rods.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Got the conduit in the ground this morning before the rain started...Pulled out wire to pull thru conduit and found that the #2 cable had been cut right in the middle of two runs. Can this THNN/THWN copper be spliced undergound?? If not guess I;ll be buying 120' run of #2 (60' x 2).

That would be expensive. Luckily things are cheaper right now than last year. Not positive, but I seem to recall that you cannot splice inside a conduit. I certainly would not do it. It would have to be a waterproof underground splice in any case, as this is a wet location.

Charles
 