After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.
After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.

After a bust on another grow house. My neighbor works for the power company and he gave me 3 rolls of #2 copper (100' - 150' rolls). Could I use this in my 2" buried conduit. It's 55' from the house to the shop sub panel.
Bevis, make sure that wire is dual rated as THWN also. If it's straight rated THHN(which I've never seen) you can't use it in a wet location(i.e. underground in conduit).
If the insulation checks out, I'd try to get 2 runs out of one of the rolls and use the #2 for a ground wire also. It'll save you from buying anymore wire.
You'll need a collar strap most likely to fit the #2 wire on your ground bar. Siemens part #ECCS1. I only remember that because I bought one this morning....![]()
You don't need to run the safety ground all the way back to the 'main'.
But you do need to drive a ground rod right near the sub-panel and attach your wire.
Just get the regular bare ground wire.
Much easier, safer, and cheaper.
Goodluck
You don't need to run the safety ground all the way back to the 'main'.
EDIT- OOPS I read it wrong. A ground wire IS required with a single 110 circuit but a ground rod is not required. That is by the ancient pre-millenium code.You may want to double check on that piece of advice.Feel free to give us examples where that would be permissable by code.
Its Now Code In Nj To Put 2 Grounding Rods 6 Ft Apart,fyi. Also Why Not Put It Through Conduit? Its Cheap And Protects The Buried Wire, Just Make Sure To Tape Your Grounds With White Tape On Both Ends Before Pulling Through The Pipe, Good Luck,mike.
Its Now Code In Nj To Put 2 Grounding Rods 6 Ft Apart,fyi. ...
Code calls for 1 rod if you can meet 23 ohms or less resistance, if not you use 2. Its simple and easier to just use 2 and as Torque eluded to some places just require 2 due to the local soil conditions. .
I didn't know that a sub panel needed it's own rod though.
.
Got the conduit in the ground this morning before the rain started...Pulled out wire to pull thru conduit and found that the #2 cable had been cut right in the middle of two runs. Can this THNN/THWN copper be spliced undergound?? If not guess I;ll be buying 120' run of #2 (60' x 2).