Wiring layout question

supratreo

Well-known member
Joined
Sep 4, 2020
Messages
354
Location
elk grove, CA
So I'm slowly wrapping up wiring my shop and and was planning a small under sink electric WH.
i ran the 6/3 for that as i had it on hand and would get the job done. while thinking about how i would need to connect this romex to the WH i realized that i may be able to reroute it to the space above the ceiling, add a box and split it 2 ways. i was already thinking about adding an outlet for a welder on the opposite side of my shop by doing a dedicated run but that would cost me a 125' roll of wire.
if i split this one it would cost me less than half that.
not only that but i can put a plug on the WH and use that outlet for welding as well. I figure this way i would get the most out of this circuit.
the WH I'm looking at draws 43A i believe, if you have opinions on these please let me know. i'lve only ever used larger, gas tankless heaters. This will just be for a hand sink in the shop.

next question is, if i am able to split this run to the other side of the shop, can i use 6/2? obviously i would mark the white conductor appropriately.
also, what size J box would i need? i've never spliced or split conductors this big but i douby a 4x4 would do it.

thanks
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
So I'm slowly wrapping up wiring my shop and and was planning a small under sink electric WH.
i ran the 6/3 for that as i had it on hand and would get the job done.
while thinking about how i would need to connect this romex to the WH i realized that i may be able to reroute it to the space above the ceiling, add a box and split it 2 ways. i was already thinking about adding an outlet for a welder on the opposite side of my shop by doing a dedicated run but that would cost me a 125' roll of wire. if i split this one it would cost me less than half that.

not only that but i can put a plug on the WH and use that outlet for welding as well. I figure this way i would get the most out of this circuit.

the WH I'm looking at draws 43A i believe, if you have opinions on these please let me know. i'lve only ever used larger, gas tankless heaters. This will just be for a hand sink in the shop.

next question is, if i am able to split this run to the other side of the shop, can i use 6/2? obviously i would mark the white conductor appropriately.
also, what size J box would i need? i've never spliced or split conductors this big but i douby a 4x4 would do it.

thanks

43a for an under the sink WH? you sure thats correct? those units are tiny. I highly doubt it draws that much for a small 1-5 gal tank. that would be way overkill. Even a 60gal tank water heater doesnt draw that much power.

what is the make and model of the WH?

if it doesnt draw that much power, 6/3 is way overkill for it and you will have issues terminating that large of wire to it
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,677
Location
S.E. TEXAS
I would do it. But i do redneck stuff all the time.
Should be fine as long as only welder or WH is not used at the same time.
I'd probably also cram it into a 4x4 deep box.
 
OP
S

supratreo

Well-known member
Joined
Sep 4, 2020
Messages
354
Location
elk grove, CA
of course.
seeing as how the welder only needs 3 conductors, i'm assuming its fine to run 6/2?
are there other ways to make the connection besides split bolt and Polaris taps?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,996
Location
NJ
Did you run 6-3 NM-B? If so, it technically by code needs to be sized at 125% which is 57.5 A. #6 Cu nm-b is only rated for 55A max. #6 Cu THHN is rated for 65A.
1769323032451.png1769323119834.png
 
OP
S

supratreo

Well-known member
Joined
Sep 4, 2020
Messages
354
Location
elk grove, CA
Thank you for that info. yes i did run6/3 NM-B. this is for a WH application only? if so, i can find one that suits the code requirements.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,708
Location
Richmond, VA
6/2 is crazy overkill for nearly all welders. You can downsize the wire based on duty cycle, but it needs to be on a dedicated circuit.

Small subpanels are cheap. If you go into it with the 6/3, then you can add a breaker for the WH (and use conduit with more flexible stranded thhn), then run a welder circuit with 10/2,or maybe even 12/2
 
OP
S

supratreo

Well-known member
Joined
Sep 4, 2020
Messages
354
Location
elk grove, CA
good point. i have a hobart 210mvp and it uses 24A. not sure why i thought i needed so much amperage.
i like the sub panel idea, i'll look into that.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,032
Location
Modesto, CA
run #6 THWN in conduit to a subpanel, then feed the WH with the same #6 THWN in conduit or youll need to use 4/3 NM-b (which is very expensive)

feed the welder from the same subpanel
 
OP
S

supratreo

Well-known member
Joined
Sep 4, 2020
Messages
354
Location
elk grove, CA
Thank you.
sounds like the 6/3 might be too much for the welder but i'll run it to the other sub just so i have it available there. i did want a small lathe and mill there at some point too.
 