Wiring over long distances Voltage Drop

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,801
Location
Connecticut
My current situation for wiring my garage requires feeds up to 145'. for my 240V lines that does not appear to be an issue since my 6 conductor #10 ga per conduit run will be capable of delivering it's derated max current of 24 amps with under 3% voltage drop.

However my 4 conductor #10 per conduit run will not be capable of delivering it's derated max current of 24 amps. The best it can do is 11 amps with under 3% voltage drop and 19 amps with 5 % VD.

Shortening the 120V line to 2 75' runs, which is very difficult will increase its capability to a more acceptable 22 amps with 3% VD.

The question is how acceptable are these numbers. Since I have seen people with twice the size garages as mine I would like to know how this situation is dealt with. Do I need to increase my wire size to #8ga for the 120V circuits.

Is 5% too much VD?

This data was calculated here.
http://www.paigewire.com/pumpWireCalc.aspx
 
To avoid these ads, REGISTER NOW!
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,801
Location
Connecticut
IMHO, no.

Remember that 5% drop is at max current. How likely are you to be operating at the max current ?

What is the VD at about 75% of max current ?

75% of max current 15 amps will be ~ 4%, 55% 11 amps is ~ 3%. Plus for this run there will be ~ 9 wire nut splices along the way.
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
Also - measure you line voltage. While this may change, it'll help you decide. Most equipment is designed for 115 volts, if you've got the full 120V (my place often measures 123V per leg) then you've got an extra 4% to work with.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
My current situation for wiring my garage requires feeds up to 145'. for my 240V lines that does not appear to be an issue since my 6 conductor #10 ga per conduit run will be capable of delivering it's derated max current of 24 amps with under 3% voltage drop.

However my 4 conductor #10 per conduit run will not be capable of delivering it's derated max current of 24 amps. The best it can do is 11 amps with under 3% voltage drop and 19 amps with 5 % VD.
...

Are you saying you are running multiple circuits to a detached building? :headscrat
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,654
Location
SE MI
Also - measure you line voltage. While this may change, it'll help you decide. Most equipment is designed for 115 volts, if you've got the full 120V (my place often measures 123V per leg) then you've got an extra 4% to work with.

Don't count on the power company to provide that 123V continuously !
 
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
Having read the OP's build thread I know this building, 30x48, has a main panel, and separate meter feed.
http://www.garagejournal.com/forum/showthread.php?t=230835

His reference to 4 conductors or 6 conductors has to do with the number of current carrying conductors in the conduit, and any associated de-rating required.

I am not understanding the distances involved unless there is some reason that outlets must be fed from only one direction away from the main panel location. If that is the case it may easier or cheaper to establish a subpanel at the other end of the building.

As has been mentioned by others, I would not be too concerned about a 5% voltage drop because of how infrequently the circuit would be loaded to maximum. If you do know of one location where this might occur, such as a table saw with high starting current, then wire it accordingly.
 
Last edited:

GarageWarrior

Well-known member
Joined
Oct 31, 2012
Messages
378
Location
Westerly, RI
BTW, in a pinch you can get a 10% buck/boost transformer to make-up for voltage drop on long runs.

10% buck/boosters are commonly used in commercial tanning booths to go from 208 to 230 volt and will also work fine with 120 power (so you get 132V before the drop) . Used ones can be had really cheap at auctions, as most guys don't know what to do with them.

A little while ago I needed to do power-washing about 200' away from the outlet and couldn't get the pump running due to too much voltage drop - added buck/booster and was back in business :rocker:
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,801
Location
Connecticut
Having read the OP's build thread I know this building, 30x48, has a main panel, and separate meter feed.
http://www.garagejournal.com/forum/showthread.php?t=230835

His reference to 4 conductors or 6 conductors has to do with the number of current carrying conductors in the conduit, and any associated de-rating required.

I am not understanding the distances involved unless there is some reason that outlets must be fed from only one direction away from the subpanel location. If that is the case it may easier or cheaper to establish a subpanel at the other end of the building.

As has been mentioned by others, I would not be too concerned about a 5% voltage drop because of how infrequently the circuit would be loaded to maximum. If you do know of one location where this might occur, such as a table saw with high starting current, then wire it accordingly.

Yes there are 120V 4 conductors in one conduit and 6 240V conductors in a separate conduit running thee perimeter of the building from one direction only. With the current limited space above the garage doors already claimed by three conduits for welder compressor and exterior lighting going around that direction if challenging but certainly not impossible and it would bring the maximum length down to about 80'. So if its not going to cause problems going one direction is preferred.

Then of course if I do find I have to bite the bullet and go over the garage doors there really is no work wasted since that conduit would end up picking up the same conduit on the other side of the garage. Its just a matter of getting through the gauntlet.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,272
Location
Modesto, CA
Why not just put a subpanel in on the opposite end of the garage and shorten your branch circuits. It will be cheaper than running all that copper around!
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,801
Location
Connecticut
Why not just put a subpanel in on the opposite end of the garage and shorten your branch circuits. It will be cheaper than running all that copper around!

How so. All that copper will still need to run the perimeter of the building. Same number of feed to stager the receptacles. Plus I will also need some heavy copper to get to the sub panel. It would reduce the gage requirements but would that pay for a sub panel and the wiring to it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,272
Location
Modesto, CA
How so. All that copper will still need to run the perimeter of the building. Same number of feed to stager the receptacles. Plus I will also need some heavy copper to get to the sub panel. It would reduce the gage requirements but would that pay for a sub panel and the wiring to it.

Al wire for the feeder to the subpanel is a lot cheaper! If youre handy with excel u could figure out if its cheaper. THHN wire adds up quick!
 
OP
6

600SL

Well-known member
Joined
Apr 26, 2012
Messages
1,801
Location
Connecticut
Al wire for the feeder to the subpanel is a lot cheaper! If youre handy with excel u could figure out if its cheaper. THHN wire adds up quick!

I can do this in my head. 2000 ft of 10 ga $400. 2000 ft of 12 ga $260 + 240 ft of 1 AGW AL $102 = $362. + subpanel, breakers, and 80 ft of 1.5" EMT > $400
 