Itzkwik said:
I'm in the process of roughing in the wiring in the garage. Trying to save a few bucks before the electrician gets here. I want to have all the wiring in place so he just has to hook up the panel box/meter, etc. The compressors I'm looking at are true 5hp. Should draw about 22 amps. I know I'll need 30 amp circuit. For 30 amp/240 do I need 10/2 or 10/3 wire?
Also want to wire for a welder so its ready when I get some extra cash. I'm looking at the Miller 175. What size wire and breaker will I need for this welder?
Thanks,
Bret
Odds are, the compressor doesn't use the netural, so all you would need is 10/2 with a ground. Make sure you re-mark the white wire ends to red. Its rare to see something like this with a netural. If you are not sure, I'd run the 10/3 w/grd and you can always fold back the netural. Might need it someday if you use the circuit for something else.
Something to consider, Compressors have high start up current draw. You are much better off to oversize the wire if there is any doubt. Also, this may not be the last compressor you ever own, you might get the itch to buy something bigger, so consider that when running wires. If the run is not too long, even 6 gauge wire would be good, then you could hook up something as big as a true 7.5 hp compressor in the future. Yes, it might cost more now, but will save hassles in the future.
I assume you are talking of a Millermatic 175 MIG welder. According to the specs on the Miller web site.........
Input Power
* Requires 1-Phase Power
* 230 V, 19.5 A, 60 Hz
So again, you will need a 30 amp breaker, and 10/2 or 10/3 wire. If the runs are very long, you need to consult the appropriate charts and tables for voltage drop, to determine if you need to possibly use 8 gauge instead of 10.
Charles