wiring size for a lift

oiler

Well-known member
Joined
Dec 21, 2006
Messages
51
Location
Cold Lake Alberta Canada
Starting to insulate my shop and i was looking at the wiring to the overhead box for my hoist
the specs for the hoist motor are 208v-230v 2HP, Single Phase, 60Hz
The wiring is a 12/2 yellow colored wire
Is this the correct size for that type of motor??
The 220 boxes in the wall all have the large conductor 4 wire going to them
Didn't want to bother the electrician unless I have to
Thanks
 
To avoid these ads, REGISTER NOW!

ArthurPE

Banned
Joined
Jun 14, 2009
Messages
423
I'm assuming the run to be less than 170' from the box, and the wire to be Cu (3% Vdrop)

per code that motor draws ~12A, so #12 rated at 20A is OK depending on the CB, starter, etc., if you have a 20A CB (or less) you are good to go...

you mean 12/2 with gnd correct?
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Just be sure and remark the ends of the white wire to red, to indicate to others later on that it is a HOT wire and not a neutral. I use a red magic marker and coat all the exposed white wire.