Wiring Switch Question

stppinz

Active member
Joined
Jan 12, 2006
Messages
28
Location
Salt Lake City
I have 4 single pole switches in a 4 guange box. All neutrals are wire nutted together, all grounded and all 4 switches are pig taled off the same power. My problem is that the power is stopped at the first switch where the power comes in. Everything works good when the first switch is on but if swith 1 is off all is off.

I know this got to be a dumb fix.

Thanks for your time

Shane
 
To avoid these ads, REGISTER NOW!

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
If all four switches are each fed off of a pigtail from the power source, this cannot be working as you describe. It sounds like the power actually passes thru the first switch first. I'd carefully recheck the wires, it sounds like the box is pretty full of wires.

Charles
 

bmwpower

Super Moderator
Staff member
Joined
Apr 24, 2005
Messages
12,578
Location
NJ
Yea, sounds like you didn't pigtail off of the source, but off of the other side. Get a meter on what you think the source feed is to see if it's hot.
 
To avoid these ads, REGISTER NOW!

index

Well-known member
Joined
Oct 5, 2006
Messages
49
do you have it like this:

__|__
| | | |

or like this:

__|__
__|_
| | |

?
the first way is correct
 
OP
S

stppinz

Active member
Joined
Jan 12, 2006
Messages
28
Location
Salt Lake City
Thanks for the replies. You are right, I think that I pig tailed off a switch leg and not the hot leg. Thanks for the help. It makes sence now.
 