I have 40 T5 fixtures I'm putting up in my shop. Each fixture has 4 bulbs. Shop is 80'x50', detached and has it's own service. Plan is 4 rows (banks) of 10 fixtures with each row controlled by it's own switch and breaker.
Due to the length of the longest runs (190'+) I want to use 240v to power them. My calcs for using 240v put me at 9 amps per row, 120v put me at 18 amps which I believe is too much for a 20 amp lighting circuit. 80% of 20 amps is 16 amps.
The fixtures I have use the Philips Advance Centium ICN-4S54-90C-2LS-G ballast that are 120v-277v. Problem is, looking at the wiring diagram on the ballast, I get no clue as to how to wire them up.
Here's a picture of the wiring diagram. And I do want 4 lamps on.
[/URL][/IMG]
On the ballast it also says, "Green terminal or ballast case must be grounded". The ballast case wedges into a slot in the fixture which has a green grounding screw.
Can some one explain to me how this ballast should be wired for 240v?
I do have 2 pole switches and breakers for each bank.
Thanks for any help,
Kevin
Due to the length of the longest runs (190'+) I want to use 240v to power them. My calcs for using 240v put me at 9 amps per row, 120v put me at 18 amps which I believe is too much for a 20 amp lighting circuit. 80% of 20 amps is 16 amps.
The fixtures I have use the Philips Advance Centium ICN-4S54-90C-2LS-G ballast that are 120v-277v. Problem is, looking at the wiring diagram on the ballast, I get no clue as to how to wire them up.
Here's a picture of the wiring diagram. And I do want 4 lamps on.
On the ballast it also says, "Green terminal or ballast case must be grounded". The ballast case wedges into a slot in the fixture which has a green grounding screw.
Can some one explain to me how this ballast should be wired for 240v?
I do have 2 pole switches and breakers for each bank.
Thanks for any help,
Kevin