hillbill9889
Active member
- Joined
- May 9, 2011
- Messages
- 28
First time poster here, lots of great information and I have read a lot here to give me plenty of information and ideas. I know many similar questions have been asked, hence the again piece.
Building a 36 x 40 garage, pictures below. I am at the point where I am doing the electrical now. I have 200 amp service to my house which is about 75 feet away. I intend to run a 100 amp subpanel out to the garage. Copper is pretty darn expensive and everything I read says aluminum is perfectly fine for this type of installation. I would prefer direct burial if possible but not worried about a conduit either. From the local electrical supply shop, I can either get 2-2-2-4 direct burial or 1-1-1-3 and put it in conduit. While I doubt I will ever draw 100 amps out here, I keep reading that due to voltage drop, the larger cable would be preferred. So, to my questions.
1) 75 foot run, buried 24", add in the actual run up the side of the garage and the house to the box adds about another 20 feet. So for this run, sounds like 1-1-1-3 really would be the best option but put it in schedule 40 conduit since I can't find direct burial right?
2) I think I saw only one post on it but it did concern me, when using aluminum, are there special breakers that need to be used at my main panel and maybe a special subpanel? The inside wiring won't be aluminum of couse, only the main feed.
3) If I use 1-1-1-3, do standard breakers/lugs support that size cable or do I need to be concerned with that?
Thanks in advance.
Oh, and pictures....




And, want to see a garage built in 1 minute?
Building a 36 x 40 garage, pictures below. I am at the point where I am doing the electrical now. I have 200 amp service to my house which is about 75 feet away. I intend to run a 100 amp subpanel out to the garage. Copper is pretty darn expensive and everything I read says aluminum is perfectly fine for this type of installation. I would prefer direct burial if possible but not worried about a conduit either. From the local electrical supply shop, I can either get 2-2-2-4 direct burial or 1-1-1-3 and put it in conduit. While I doubt I will ever draw 100 amps out here, I keep reading that due to voltage drop, the larger cable would be preferred. So, to my questions.
1) 75 foot run, buried 24", add in the actual run up the side of the garage and the house to the box adds about another 20 feet. So for this run, sounds like 1-1-1-3 really would be the best option but put it in schedule 40 conduit since I can't find direct burial right?
2) I think I saw only one post on it but it did concern me, when using aluminum, are there special breakers that need to be used at my main panel and maybe a special subpanel? The inside wiring won't be aluminum of couse, only the main feed.
3) If I use 1-1-1-3, do standard breakers/lugs support that size cable or do I need to be concerned with that?
Thanks in advance.
Oh, and pictures....




And, want to see a garage built in 1 minute?